You should be able to go to 32kW with four Outback Radians. I agree, there are not enough 32-100kW split phase inverter system options. With LiPO batteries becoming popular, a high integrated charging capacity is desirable in larger battery capacity scenarios, especially if trying to maximize generator efficiency through reduced run time.
On Sun, Feb 23, 2020 at 12:03 PM Jeff Clearwater < [email protected]> wrote: > The Victron Quattro (120/240) is stackable to 6 units for 30 KW of split > phase or 48 KW of 240V and 144KW of 3 phase if I’m reading the spec sheets > correctly. > > Sent from my iPhone > > On Feb 23, 2020, at 6:42 AM, Jay <[email protected]> wrote: > > People might also look at Victron inverters. > > Jay > Peltz Power. > > On Feb 23, 2020, at 3:23 AM, Jeff Clearwater <[email protected]> > wrote: > > The Sol-Ark manual indicates 240 Volt stacking to 8 units (9 units for > 208V). They list the "12KW" off-grid output as 8 KWs each. So 64 KWs. > > anybody stacked a signficant number of them yet? > > Looking forward to hearing feedback from experienced installers. > > Best, > > Jeff > > > Allan Sindelar wrote on 2/22/20 6:56 PM: > > > Jeff, according to Midnite’s website, their B-17 inverter can be up to 40 > kW in 2 kW increments. > Allan > > On Feb 22, 2020, at 8:05 PM, Jeff Clearwater > <[email protected]> <[email protected]> wrote: > > Ahh you're right all our 120/240 volt systems are less than 24 KW. I > was thinking of 230 V 50hz systems with multi-cluster boxes. > > How large can the Sol-Ark be stacked to? Anyone with large Sol-Ark system > experience? > > I hear Mornignstar and MidNite are working on surge capable off-grid > inverters. Anyone have a insight as to their KW goals? > > Best, > > Jeff > > wes kennedy wrote on 2/21/20 1:37 PM: > > Hi Jeff, > > I think the biggest split phase sunny island system is 4 units, so that's > 24KW. > > What do you do for larger systems? Segment the loads? Not always very > practical. > > This latest opportunity is for an agricultural building that peaks at > 75KW. > > > > -Wes Kennedy 303-653-3073 > > > On Friday, February 21, 2020, 12:47:39 PM MST, Jeff Clearwater > <[email protected]> <[email protected]> wrote: > > > All of my SMA Sunny Island Sunny Boy AC coupled systems greater than 12 KW > have worked flawlessly and delivered reliable power and good monitoring for > years. Less excited about my Schneider and Outback systems due to > callbacks and hassles. a bit more expensive but worth it IMHO. > > Hope that helps! > > Jeff > > wes kennedy wrote on 2/21/20 9:41 AM: > Hi friends, > > I keep running across opportunities with 50KW-300KW peak load > requirements, on split phase services. Big homes, agriculture etc. > > Outback, Schneider, SMA can all gang/stack into the 30-50KW range, but > north of there, I am not finding many (any?) options? > > Just found Aims Power 50 KW split phase unit with claims of higher power > offerings by special order. Even the 50KW unit is $20K, so quite spendy. > Any experience with these guys? > 50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO > 220/230/240 Vac > <https://mailtrack.io/trace/link/4f7d32cc7dfc2842fab2bf9bea74770d093aa180?url=https%3A%2F%2Fwww.aimscorp.net%2F50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html&userId=1613865&signature=4c8e36397e811f06> > > > > > 50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO ... > > 50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc Split > Phase 220/230/240 > > <https://mailtrack.io/trace/link/216c9b2fbb26a7942bdc584da32840a0a0ef7fd7?url=https%3A%2F%2Fwww.aimscorp.net%2F50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html&userId=1613865&signature=946f0bcf0459019e> > > > Thanks for any input! > > -Wes Kennedy 303-653-3073 > on this list since the 90's > > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & > settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <https://mailtrack.io/trace/link/d63d3e3a978e8a87add1f7501d59ee5f5fb38a4f?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4973675a4c4ab420> > > List-Archive: > http://www.mail-archive.com/[email protected]/maillist.html > <https://mailtrack.io/trace/link/7a023e95bffe7d2040feac93f95e0a0f11fa6987?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=46b10739ff5fd8bf> > > List rules & etiquette:www.re-wrenches.org/etiquette.htm > <https://mailtrack.io/trace/link/331c727f2364456812baea8d1c52d3f40beb8a90?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=e719e1d05b5cf87c> > > Check out or update participant bios:www.members.re-wrenches.org > <https://mailtrack.io/trace/link/5bb69b1b7b0444267f727e13eb46e364a9678425?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=957b8e96e1dc8c0b> > > > -- > ~~~~~~~~~~~ > Jeff Clearwater > Village Power Design > linkedin > <https://mailtrack.io/trace/link/bd394429f8487d697d00a1e7111da004066652d3?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Fjeff-clearwater-0622a312%2F&userId=1613865&signature=36a1593bd28b8ccd> > www.villagepowerdesign.com > <https://mailtrack.io/trace/link/cecd4177686007dbcca9514d9fe8dace135819a2?url=http%3A%2F%2Fwww.villagepowerdesign.com&userId=1613865&signature=1d41a5257aa87e38> > cell - 413-559-9763 > ~~~~~~~~~~~~~~~~~~~~~~~ > > > > -- > ~~~~~~~~~~~ > Jeff Clearwater > Village Power Design > linkedin > <https://mailtrack.io/trace/link/c380a264fce7d248a05288cd74b288d2284afd86?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Fjeff-clearwater-0622a312%2F&userId=1613865&signature=0979b1caceaf1f78> > www.villagepowerdesign.com > <https://mailtrack.io/trace/link/3404019e669b4ea32e8ec188a6f79c661abb162a?url=http%3A%2F%2Fwww.villagepowerdesign.com&userId=1613865&signature=4df2961ce5ac7182> > cell - 413-559-9763 > ~~~~~~~~~~~~~~~~~~~~~~~ > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <https://mailtrack.io/trace/link/885b9b3aa7dcee55c3030e4c1ac895732d0f9476?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=8f65292e04db6d22> > > List-Archive: > http://www.mail-archive.com/[email protected]/maillist.html > <https://mailtrack.io/trace/link/22484a017da9b2eebda0840b01f4505fd97cb56a?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=a94f136f8720e27b> > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > <https://mailtrack.io/trace/link/0dffba0ee72532b58372452ce5beb1bae3ba7e59?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=ff4d9ed34e66d68e> > > Check out or update participant bios: > www.members.re-wrenches.org > <https://mailtrack.io/trace/link/d4456b7a80863a1217d1086fe7653505897d9538?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=8f0b6b1530f7ed66> > > > > -- > ~~~~~~~~~~~ > Jeff Clearwater > Village Power Design > linkedin > <https://mailtrack.io/trace/link/5e21bee273ab6ea4ea7bb66af2f6a77bba39d0e4?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Fjeff-clearwater-0622a312%2F&userId=1613865&signature=67970ca7721852f4> > www.villagepowerdesign.com > <https://mailtrack.io/trace/link/25079fe30279c8e43717988138da7a1d6a849278?url=http%3A%2F%2Fwww.villagepowerdesign.com&userId=1613865&signature=f94c7714ce45bcb0> > cell - 413-559-9763 > ~~~~~~~~~~~~~~~~~~~~~~~ > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <https://mailtrack.io/trace/link/7faad24744f7836e52eb63cdd3a76a23937d9e54?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=21af3aeef94a045b> > > List-Archive: > http://www.mail-archive.com/[email protected]/maillist.html > <https://mailtrack.io/trace/link/f41cc1c5b8afe2e101843a6b8ec945448ece91a5?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=45e6f26912d973bb> > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > <https://mailtrack.io/trace/link/b7f9144a00a6cf0b4d6f2bd681111b53a6595f2e?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=088a691258bf6bd1> > > Check out or update participant bios: > www.members.re-wrenches.org > <https://mailtrack.io/trace/link/2d2f5cd7b9bb563906971321e447e25526729513?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=160320716001b611> > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <https://mailtrack.io/trace/link/ebd1d876c5b86898cb21857244c50fc53146cb96?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=57c4997a6aa1dbab> > > List-Archive: > http://www.mail-archive.com/[email protected]/maillist.html > <https://mailtrack.io/trace/link/6fda109b28cb801bcbaed4a78cee18a7e17ee42f?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=d1de0d71cffe8980> > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > <https://mailtrack.io/trace/link/ce5dcc918dfb2fa6cfd75d08dde8184ca14e53a8?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=35554bed0717d9b9> > > Check out or update participant bios: > www.members.re-wrenches.org > <https://mailtrack.io/trace/link/703ff1acec2d0f28815a2ab2d7b103da71aa4216?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=e961529dbea97b88> > >
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org