In general, both.
This ag opportunity is to load shift out of TOU zone, but wants resiliency too.
-Wes Kennedy 303-653-3073
On Friday, February 21, 2020, 02:56:23 PM MST, Harry Mahon
<[email protected]> wrote:
Wes – Indeed, max Sunny Island 240VAC cluster is 4 units, so 23kW max BATTERY
power.
Limit of roughly 27kW of PV (4x 120V x 56A relay limit = 26,880W) with that
cluster if grid-tied with backfeed, so around 50kW max daytime load offset per
cluster. That may help if peak loads are always daytime?
Are you trying to take these systems off-grid, or just reduce peak load?
Best regards –
Mike
SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300
Rocklin, CA 95765
U.S.A.
Mobile: +1 916 918 9412
www.SMA-America.com
Solar Academy: https://solaracademy.sma.de/en.html
SMA America Solar Academy webinars: https://solaracademy.sma.de/en/courses.html
Choose "United States"
This email and any attachments thereto may contain SMA America, LLC
confidential, privileged and private material for the sole use of the intended
recipient. Any review, copying, or distribution of this email (or any
attachments thereto) by others is strictly prohibited. If you are not the
intended recipient, please contact the sender immediately and permanently
delete the original and any copies of this email and any attachments thereto.
Thank you.
From: RE-wrenches <[email protected]>On Behalf Of wes
kennedy
Sent: Friday, February 21, 2020 2:38 PM
To: RE-wrenches <[email protected]>; Jeff Clearwater
<[email protected]>
Subject: Re: [RE-wrenches] High Power Split phase inverter/chargers
Hi Jeff,
I think the biggest split phase sunny island system is 4 units, so that's 24KW.
What do you do for larger systems? Segment the loads? Not always very
practical.
This latest opportunity is for an agricultural building that peaks at 75KW.
-Wes Kennedy 303-653-3073
On Friday, February 21, 2020, 12:47:39 PM MST, Jeff Clearwater
<[email protected]> wrote:
All of my SMA Sunny Island Sunny Boy AC coupled systems greater than 12 KW have
worked flawlessly and delivered reliable power and good monitoring for years.
Less excited about my Schneider and Outback systems due to callbacks and
hassles. a bit more expensive but worth it IMHO.
Hope that helps!
Jeff
wes kennedy wrote on 2/21/20 9:41 AM:
Hi friends,
I keep running across opportunities with 50KW-300KW peak load requirements, on
split phase services. Big homes, agriculture etc.
Outback, Schneider, SMA can all gang/stack into the 30-50KW range, but north of
there, I am not finding many (any?) options?
Just found Aims Power 50 KW split phase unit with claims of higher power
offerings by special order. Even the 50KW unit is $20K, so quite spendy. Any
experience with these guys?
50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO
220/230/240 Vac
|
|
|
| | |
|
|
|
| |
50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO ...
50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc Split
Phase 220/230/240
|
|
|
Thanks for any input!
-Wes Kennedy 303-653-3073
on this list since the 90's
_______________________________________________ List sponsored by Redwood
Alliance List Address: [email protected] Change
listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or
update participant bios: www.members.re-wrenches.org
--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin
www.villagepowerdesign.com
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org