Drake, I concur with your approach on this item -

1.  Either the shock hazard was reduced by NEC 690.12 with MLPE for the
workers *too* or folks have been qualified persons in accordance with NEC
690.4(C) to recognize and avoid the shock hazard for string inverters.

2.  Specifically, there's this incident on the list found here:
https://www.osha.gov/pls/imis/accidentsearch.accident_detail?id=101927.015
In other words, would this incident have been minimized with the use of
MLPE?

On Wed, May 6, 2020, 5:41 PM <[email protected]> wrote:

> Interestingly enough, the data on the link
> <https://www.osha.gov/pls/imis/AccidentSearch.search?p_logger=1&acc_description=&acc_Abstract=solar&acc_keyword=&sic=&naics=&Office=All&officetype=All&endmonth=05&endday=05&endyear=2002&startmonth=05&startday=05&startyear=2021&InspNr=>
>  provided
> shows accidents from gas explosions, falls, health problems and  industrial
> injuries. None of these incidents could have been prevented by module level
> power electronics. This is typical of the data that I've seen so far.
> ---
>
>
>
> On 2020-05-06 17:22, Martin Herzfeld wrote:
>
> There could be an issue of encouraging MLPE for worker safety?
>
> 1.  This is data involving incidents with workers in the OSHA Fatalities
> and Catastrophe Investigation Summaries found here:
>
> https://www.osha.gov/pls/imis/AccidentSearch.search?p_logger=1&acc_description=&acc_Abstract=solar&acc_keyword=&sic=&naics=&Office=All&officetype=All&endmonth=05&endday=05&endyear=2002&startmonth=05&startday=05&startyear=2021&InspNr=
>
> 2.  In the past I've observed an arc fault at the module level with
> traditional string systems without a listed arc-fault circuit interrupter
> NEC/CEC 690.11. The function in NEC/CEC 690.12 would be - to *reduce the
> shock hazard *- for *emergency responders* or *firefighters? (NEC 2020).*
> However, I've observed thermal events in the panelboard with plans and
> workmanship issues.
>
> On the other hand, falls are the #1 reason for incidents in the
> construction industry.
>
> All the best,
>
> Martin Herzfeld, Interstate Renewable Energy Council (IREC) Certified
> Master Trainer ™ for Photovoltaics (PV) Installation Professional #IREC
> 10037
> Contract Training Provider (CTP)
> Adjunct Professor, Energy
>
> California Solar & Electrical Contractor License  #00833782  C46, C10,
> D56, D31, C-7 - Since 2004
> Solar, Electrical, Trenching, Pole Installation & Maintenance,
> Instrumentation
>
> Contract Solar (PV) Technical Inspector - 3rd Party Inspections
> Underwriters Laboratories (UL) Certified PV Installer #17, OSHA 30
> OSHA-Authorized Construction Trainer #32-0105338
> CompTIA Certified Technical Classroom Trainer (CTT+) #T3NSZCNBBKB4QTQG
>
> * Professional Member, International Association of Electrical Inspectors
> #7035507 - Since 2006
> * Accredited and Registered North American Board of Certified Energy
> Practitioners (NABCEP) Continuing Education (CE) Training Provider
>
>
> On Thu, Apr 30, 2020, 8:29 AM <[email protected]>
> wrote:
>
>
> I would like to see real data on the fire risk of string inverters.
> Anecdotal problems are not data.
>
> The industry is definitely heading toward MLPE due to the rapid shutdown
> requirements. In many cases MLPE makes sense, in other cases it doesn't.
>
> Systems that are more cost effective and reliable can often be built by
> using string inverters.
> ---
>
>
>
>
> On 2020-04-29 22:05, Jason Szumlanski wrote:
>
> "Rapid Shutdown does not prevent fires."
>
> Not true. If the effect of RS is to steer the market to MLPE, I believe it
> has a significant impact on reducing fire risk. As one who has watched a DC
> conductor fire smolder out of control, I am sold on an AC module or
> microinverter architecture. While RS on a DC array doesn't necessarily
> reduce fire risk within the array, it still has the potential to reduce
> severity and spread. Nothing is going to prevent all fires. I get that.
> We're talking about risk mitigation when it comes to RS.
>
> As for "dependable string inverters," the one dependable feature is
> failure at least once in the module lifetime, accompanied by a shocking
> repair bill.
>
> I'm not a shiny object following kind of guy, but the writing is on the
> wall. MLPE is the future. Modular, serviceable, disposable if you will.
> Like it or not, Edison is going to lose this battle to Tesla (Tom vs
> Nikola). And I live less than 5 minutes away from Tommy E's winter home in
> Fort Myers, FL. And I "grew up" in the industry living off-grid in DC
> power. But AC distribution wins for safety at various scales.
>
>
>
>
>
>
> On Wed, Apr 29, 2020, 9:42 PM <[email protected]>
> wrote:
>
> Rapid Shutdown does not prevent fires; it was originally drafted to allow
> firefighters to vent a roof without being hindered by energized PV arrays.
> This rule was expanded to include other DC wiring from PV sources.
>
> As for PV safety, I'd like to see some significant, statistical evidence
> that shows there is a major fire danger from PV relative to other sources.
> A fire from a solar array gets a lot more press than one from a gas leak,
> bad wiring or an ash tray emptied into a wastepaper basket.
>
> Large public buildings should have all the protection that is available.
> Does one size fit all?
>
> Would it be reasonable to allow residential installations under 12 kW,
> with 1/4 of the roof adjacent to the array available for venting, to be
> excepted from 690.12? What about sparsely occupied commercial buildings
> with ample roof area open for ventilation?
>
> Many of us have chosen to work with renewable energy technology to lessen
> the harms caused by fossil fuel extraction and combustion. The need for
> non-carbon based energy sources has become extremely clear.
>
> The old string inverters still chug along year after year, with little or
> no maintenance. Someone must pay for the ongoing maintenance of module
> level electronics. Dependable string inverter systems should be allowed
> unless statically significant danger can be demonstrated.
>
> Drake
> ---
>
>
>
> On 2020-04-29 16:01, Jason Szumlanski wrote:
>
> I have been to several PV fires for string inverter systems, both
> commercial and residential, and have seen many DC systems at serious risk
> of fires or in various stages of melted insulation and connectors. Most of
> these systems have exhibited good to excellent workmanship. Things just
> went wrong. Some were traceable to animal damage, wind, or other
> unmitigated factors, and some were unexplained. I disagree that there isn't
> justification for rapid shutdown.
>
> In my opinion, what we need is some additional innovation and competition
> in the MLPE space. Reliability is clearly a key factor, but there is no
> denying that MLPE has added safety benefits among other benefits. And if
> you do enough volume and set up your business for efficiency
> (standardization of product offerings), MLPE isn't much more expensive. It
> becomes a negligible cost relative to the benefit. The value proposition is
> easy to convey. There are limits to this, but for the majority of
> residential and small commercial installations, MLPE has become the de
> facto standard around here. String inverters are dinos, and replacing 8-12
> year old transformer based inverters is many times more annoying than some
> MLPE swaps. I will admit that the roofs around here are pretty easy to
> walk, so that is a factor that might not apply to you.
>
> If you go under due to manufacturer product failures, you are not writing
> your contracts right or not charging enough for service issues beyond your
> control. I believe that's a red herring. You might suffer some reputation
> damage, but for someone that has been installing MLPE for over a decade,
> that is totally manageable. Consumers find a service call to replace MLPE a
> LOT more palatable than a surprise inverter replacement that could cost
> thousands of dollars. People just don't plan for that.
>
> Regarding rapid shutdown devices, I have also come across a few that
> "someone" has bypassed around here. I don't know if they were never
> installed properly or disabled/bypassed due to failure. It seemed
> suspicious to me at the time. I remember that it made me wonder what good
> is a rapid shutdown device if it is easily defeated? That's another
> argument for MLPE. It has pretty failsafe MLPE functionality.
>
> Jason Szumlanski
> Florida Solar Design Group
>
>
>
> On Wed, Apr 29, 2020 at 10:59 AM <[email protected]>
> wrote:
>
> Clearly, rapid shutdown increases cost and reduces reliability. Given the
> excellent safety record of PV, prior to rapid shutdown being required, it
> is unnecessary. The few anecdotal incidents of PV fires were not enough to
> justify the requirement, especially on smaller systems.
>
> According to a friend who worked for a local installation company that
> went under, a big part of the reason for their failure was the chronic
> replacement of microinverters and optimizers.
>
> What steps can be taken to create some balance in the rapid shutdown
> requirements that are in the NEC?
>
>
> ---
>
>
>
> On 2020-04-29 07:27, Sky Sims wrote:
>
> So far rapid shutdown has been a nightmare. It's added a lot of cost for
> no measurable benefit.
> Using always off devices like midnight solar and Tigo makes it impossible
> to test open circuit voltages. Which opens the door to tons of problems
> when commissioning systems.
> Also we've been trying out midnight Solar's product and have had an absurd
> failure rate. Which means lots of truck rolls and troubleshooting and
> system downtime. They send replacement product but they aren't paying for
> the lost weeks of productivity.
> We have Tigo product in hand and are deciding which project to try it on.
> But our big concern about using it is not only the inability to confirm
> open circuit voltage of the strings but also the way panels bypass if the
> device doesn't allow the panel to connect properly. Both of these features
> are a recipe for problems and potential troubleshooting nightmares. The
> warranty from Tigo doesn't cover our expense if the product fails. And
> that's really what our reservations about the product boil down to right
> now. If we're on a job with 50 units and one fails, the contractor or the
> homeowner will be the ones eating the expense of finding it and replacing
> it. There has to be a better option.
>
> Sky Sims
> Https://EcologicalSystems.biz
>
> On Apr 28, 2020, at 7:46 PM, Corey Shalanski <[email protected]> wrote:
>
> Now that 690.12 of the *NEC* 2017 has been in effect for several years, I
> am curious how designers and installers are meeting the associated
> requirements with string inverter-based systems (*not* considering
> microinverters or DC optimizers). I am generally a fan of the KISS
> principle, and as best I can determine the *Tigo* TS4-F device is one of
> the simplest options currently available on the market. What are others
> finding?
>
> I'd love to hear about favored options for complying with rapid shutdown.
> Any success stories? or better yet, any early failures?
>
> --
> Corey Shalanski
> Jah Light Solar
> Portland, Jamaica
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/48741004c205351e1fd6a97d2252c71188d81e71?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=56977124ac95b63a>
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
> <https://mailtrack.io/trace/link/b02b5a7da549db8b06246de6ff83408a2d397f16?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=2505444a6c7e76e8>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/14307b48a5cf21a014a9767754fb9e3faa3e7b78?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=c9675ece76eedbfe>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/917ce495ba8f7369e01489e6fbe01e0c529c5c1a?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=f07b8c2e5b7272c1>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/53e92374f477c4523c84f04b60d9235e042fe484?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=05c2b8925c2cca9b>
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
> <https://mailtrack.io/trace/link/64b8ad23a59b7db17c7803f561209f2ec8fcd931?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=851e5d5b1ad7c5c6>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/1b9d76c7044d5f000ec9d0dc76ffe05711e667c0?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=06c42b3c6357f539>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/df315d52bf0b1d7387cef78766012f742e8a6642?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=c3967f238393d77c>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/293b35354380ac1970c6a01c39adb66144564dbf?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=733dc831fc029701>
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
> <https://mailtrack.io/trace/link/4b39d310624bc3f043f6541c22bd38f7ae43620b?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=4568169f724351ec>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/1a3c4c9b301c7d3a44855867469231a53c1de036?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8d57f550c03f31fc>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/55a1c3702348098b72ae7057204e6fe1c0ee44ad?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=81fe3e4f78a351f9>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> Y
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to