Hello All


1.        I want to avoid AFCI unless mandated.  Will this be defeated if I 
don’t run the leads through the sense coil? (There is an AFCI and non-AFCI 
version but I can’t seem to find the non-AFCI version anywhere.)

     *   Yes, you can bypass the AFCI by simply not running the PV conductors 
through the sensor coil



2.        I noticed the manual indicates you are not supposed to mix the FM100 
with the FM80 or 60 in the same battery system.  This negates it for one 
project I had in mind.  I am curious as to why this is.  Anyone know?

     *   Here is a link to an App note that covers this situation
     *   
http://www.outbackpower.com/downloads/documents/appnotes/fm100_fm80_app_note.pdf
     *

3.        Will the FM100 work with a standard hub?

     *   Yes, both HUB4 and HUB10.3, but firmware updates take almost an hour 
on the HUB4 because it’s slower.
     *

4.        I suppose this unit requires a 125 amp breaker.  If the PV array 
cannot support that full 100 amps I might down-size the OCPD accordingly.  
Anyone contemplate this question?

     *   Depends on the application, but all of our prewired load centers and 
systems come with 125A breakers.




I hope this helps take care all.




From: William Miller <[email protected]>
Sent: Thursday, May 14, 2020 10:49 PM
To: RE-wrenches <[email protected]>
Subject: Outback FM100

Friends:

I have occasion to try the FM100 charge controller.  I am wondering of anyone 
had found any quirks with implementing this device.  I have a few specific 
questions:


  1.  I want to avoid AFCI unless mandated.  Will this be defeated if I don’t 
run the leads through the sense coil? (There is an AFCI and non-AFCI version 
but I can’t seem to find the non-AFCI version anywhere.)
  2.  I noticed the manual indicates you are not supposed to mix the FM100 with 
the FM80 or 60 in the same battery system.  This negates it for one project I 
had in mind.  I am curious as to why this is.  Anyone know?
  3.  Will the FM100 work with a standard hub?
  4.  I suppose this unit requires a 125 amp breaker.  If the PV array cannot 
support that full 100 amps I might down-size the OCPD accordingly.  Anyone 
contemplate this question?

Thanks in advance.
William


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to