Mark,

It is conceivable to use Li-ion without protection. To do so you must ALWAYS 
guarantee that you will not over charge, over current, over discharge or charge 
frozen cells…ever. This is a 0 tolerance rule. In a RE system, how can you be 
100% sure? 

Modest rates is not the issue. It’s already difficult to overcurrent the GBS 
cells. Over voltage a cell just once and you can cause damage or possibly fire. 
Similarly, if you over discharge a cell just once you can damage it and may 
cause a future fire while charging it normally.

Cell balancers only reduce a small amount of current on a single cell that is 
becoming saturated. It won’t stop over voltage.

To my knowledge there is no safe way to have a Li battery system without 
BMS/EMS unless you are always in control of charge/discharge events. 

Scold…now that you know, yes, consider yourself scolded.

Larry Crutcher
Starlight Solar Power Systems



On May 26, 2020, at 12:24 PM, Mark Frye <[email protected]> wrote:

Thanks Larry,

I am familiar with GBS cells. Would you scold me too badly if I told you my 
thought that with modest discharge rates and on the charge side, with cell 
balancers installed, and limiting the charge current to 15A, one doesn't really 
need the BMS for the 60AH pack? 

On 5/26/2020 10:47 AM, [email protected] 
<mailto:[email protected]> wrote:
> Hi Mark,
> 
> One of the many benefits of Li-ion is the ability to provide much higher 
> continuous current than any comparable size LA battery.  
> 
> You don’t need more than 2kWh (40Ah) and want to know the smallest battery 
> you can use. To directly answer your question: A 60AH Elite Power Solutions 
> (GBS cells) battery bank @ 48V has about 3 kWh of energy storage. This is a 
> tiny battery bank, just 20”L x 11”W and weighs only 80 pounds. However, it 
> can provide a whopping 9kW (3C) continuous output and up to 31kW momentarily! 
> Thats much more than you will likely ever use. 
> 
> Though hard to imagine, this will work with your inverter. We have built 
> several 3kW inverter systems @ 12V with a single 100AH battery for starting 
> heavy loads like air compressors and air conditioners. No problem. Whether 
> this is the “best practice” will require more discussion. Let me know if you 
> need more detailed help as we have many years experience with Li-ion battery 
> systems.
> 
> Larry Crutcher
> Starlight Solar Power Systems
> 
> From: Mark Frye <[email protected] <mailto:[email protected]>>
> Subject: [RE-wrenches] How much Li battery?
> 
> In the way back machine I remember being at a product roll out meeting 
> for the brand new Outback FX inverter. I asked the engineer, what was 
> the smallest battery bank that could be connected to the inverter. He 
> said on the fly that probably you would want the battery to "weight" at 
> least as much as the inverter. I thought that was a great answer.
> 
> Fast forward, with a 4000w Outback Radian, AC coupled with 2000w of PV, 
> what is the smallest Li battery I would want for stable operation?
> 
> My loads don't really need more than 40ah of capacity.
> 
> What is the latest best practice on this?
> 
> Thanks.
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to