Yes, that is an aspect to this but not the root cause of the problem I am 
having.

 

The product manager explained that because the LG battery has an internal DC to 
DC converter, when it switches between charging and discharging, there is a 
appx 3 second loss of power when in backup mode. He described how one setup 
could be 2xLG Resu and 1x BYD as the BYD maintains constant voltage and no 
“lag.”

 

Still, my own personal LG in a StorEdge system has absolutely no issue like 
this so I’m trying to figure out why this is a challenge in SMA but not 
SolarEdge.

 

But back to my main problem, which is charging of the battery in backup mode, 
from the PV inverter. I am still awaiting his promised email, but he discussed 
setting country code to Ca Rule 21 to soften the charging points. He said 
setpoints for when to cease recharging (to prevents too high charging) is field 
adjustable but I find the SMA interface to be a complex, PhD level of 
complexity without much installer-level explanation.

 

He also said if any of the three batteries were at this no-charge setpoint, 
this might cease PV charging so I’ll check that and if that the case, I’ll turn 
oof high SoC batteries and try to bring all up to common level. I sure hope 
this is not the case because that would be a serious software gap.

 

I’ll share more as I get more info or learn more in the field.

 

Scot Arey

 

From: RE-wrenches <[email protected]> On Behalf Of 
Jerry Shafer
Sent: Friday, July 10, 2020 6:01 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] SMA Sunny Storage AC-coupled with SB6.0 won't 
recharge LG Resu batteries during backup ops

 

Scott, Wrenches

We have had systems with the SMA storage but we have used the BYD and have had 
no problems so far with recharge and operations all as expected, it may be an 
issue with LG programming and the SMA not communicating properly

JUerry  

 

On Fri, Jul 10, 2020 at 2:57 PM <[email protected] 
<mailto:[email protected]> > wrote:

We have a design with Sunny Storage 6.0 inverter, SB 6.0 PV inverter, the SMA 
Automatic Backup Unit, and three LG Resu batteries. Works like a charm during 
normal grid ops but when it goes into backup ops, the Sunny Storage increases 
frequency to between 60.6 with blips up to 61 hertz, resulting in the PV 
inverter throttling back from 5,000+ watts to between 1,300 to 345 watts.

 

The result is that the batteries do not recharge from the PV during backup 
mode, even when SoC is less than half capacity. This also means the max power 
through the ABU to the “whole house backup” is the 6,000 watts from the Sunny 
Storage plus the (very) retarded power output of the SB PV inverter.

 

SMA tech support just said, “that is normal, the LG Battery is the culprit and  
does not charge from PV in this setup.”

 

I was stunned because why else would I buy this ABU coupling setup…Anybody have 
any ideas? I’m hoping the Sunny Storage freq shifting ramp-up parameters can be 
adjusted so that PV inverter operations continue when the battery is at a less 
than full SoC.

 



 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]> 

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> 

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to