3 years in service now & no service required or needed. I installed a large 
-120 gallon well expansion tank as usual [Typ off grid thinking -- reduce the # 
of start surge] & found out it was not necessary. The start up is so tapered 
smooth that I could have used a 40 gal tank, when I spec another OG system I 
will not use an oversized storage tank. Ghost load on the controller [super 
smart, digital & always awake] is very slight. The controller uses a transducer 
not a pressure switch measures PSI in tenths of a PSI.  I have not tried to 
measure the controller load asleep, as it is hard wired in.



Dana Orzel                              Great Solar Works, Inc. 
C - 208.721.7003                       [email protected]
Idaho Contractor - # 028765         Idaho PV # 028374
NABCEP # 051112-136                       www.solarwork.com
"Responsible Technologies for Responsible People since 1988"  
 Please consider the environment before printing this email.


-----Original Message-----
From: RE-wrenches <[email protected]> On Behalf Of 
frenergy
Sent: Tuesday, September 22, 2020 7:18 PM
To: [email protected]
Subject: Re: [RE-wrenches] Pentair Pump power

Just curious, the 120VAC 1/2 HP submersible that has to date been in the well 
for the last 17 years has needed zero service, is there something about the 
Pentair set-up you're referring to that needs regular or occasional service?  
Believe me I understand your comment about schlepping service to some other 
poor soul, but....

Is the Pentair powered with 240 Vac inverter power?

Bill

On 9/22/2020 2:58 PM, Dana Orzel wrote:
> If you have 240 VAC look at the Pentair wild AC pumps I have one at 20 GPM 
> and am a believer. Tapers on - soft start, varies the volts & amperage with 
> flow and tapers the amperage down as it reaches a full expansion tank.
>
> Even better my local well pump installer sells & services it so I do not have 
> to! Getting a little smarter as I get older.
>
>
>
> Dana Orzel                              Great Solar Works, Inc.
> C - 208.721.7003                       [email protected]
> Idaho Contractor - # 028765         Idaho PV # 028374
> NABCEP # 051112-136                       www.solarwork.com
> "Responsible Technologies for Responsible People since 1988"
>  Please consider the environment before printing this email.
>
>
> -----Original Message-----
> From: RE-wrenches <[email protected]> On 
> Behalf Of frenergy
> Sent: Tuesday, September 22, 2020 1:12 PM
> To: [email protected]
> Subject: [RE-wrenches] Pump power
>
> Wrenchers,
>
>               We're upgrading an off-grid water system.  Dynamic head 
> while pumping at 20 GPM is 150 ft from water level to wellhead and 
> then its 85 ft vertical to storage tank so 235 ft total head to open 
> discharge.  We would like to get most of that 20 GPM, we need to know 
> if there is personal experience with starting a 1.5 or 2 HP, 240 vac, 
> 2 wire submersible pump against that kind of head with an Outback Flex
> Power2 (2 X VFXR3648A-01 inverters).
>
>               The FP2 will also be powering standard off-grid loads. There is 
> plenty of battery behind the inverters.  If a soft-start solution is 
> required, some specifics would be great. Grundfos doesn't seem to have an 
> option for these requirements, solar-direct is not an option at this location.
>
> Thanks,
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
>
> --
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
--
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net


-- 
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to