AEP Won't let us do a line side tap. We can tap into the line side and
install another service as permitted by the Rule of Six. I have used the
Eaton, 4 space breaker box with 2 spaces for the service disconnect and
2 for the PV connection.
Supposedly you can use a main breaker retainer, according to Eaton tech
support, However, the box doesn't have holes for the screws, but you can
drill a hole in the box and get one screw in. It seems to hold the
breaker firmly.Some inspectors could have an issue with that.
Other manufacturers may have better solutions.
---
On 2020-10-27 18:27, Kristopher Schmid wrote:
Hi All,
I have a utility that is hinting that they are going to deny my interconnection application with a supply side connection and require a load side. Has anyone seen this before?
(Proposed interconnection would be with Milbank step lugs in a 200 A socket and a 60 A fused disconnect within 10 feet.)
If they refuse it, i am thinking that registering a complaint with the Wisconsin PSC may be appropriate.
Kris
Shine On!
Kris Schmid
Legacy Solar, LLC
137 West 1st Avenue
Luck, WI 54853
www.legacysolar.com [1]
715-653-4295
NABCEP Certified PV Installation Professional
Licensed Wisconsin Master Electrician
BSEE
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Links:
------
[1] http://www.legacysolar.com
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org