There's very "territorial" language in the 2020 NEC 705.11(D):

"For meter socket enclosures or other equipment under the exclusive control
of the electric utility, only connections approved by the electric utility
shall be permitted."

Brian Mehalic
NABCEP Certified Solar PV Installation Professionalā„¢ R031508-59
National Electrical CodeĀ® CMP-4 Member
(520) 204-6639

Solar Energy International
http://www.solarenergy.org

SEI Professional Services
http://www.seisolarpros.com



On Wed, Oct 28, 2020 at 9:00 AM Kristopher Schmid <[email protected]>
wrote:

> Thanks for all the discussion and insight.  I believe the main issue here
> is them being territorial about the meter socket (they did not install it
> and they do not own it).  My follow up question to them was, "I assume that
> you allow a 320 A meter socket feeding two main panels.  Is this
> different?"  Waiting for a response...
>
>
> Shine On!
>
> Kris Schmid
> Legacy Solar, LLC
> 137 West 1st Avenue
> Luck, WI 54853
> www.legacysolar.com
> 715-653-4295
> NABCEP Certified PV Installation Professional
> Licensed Wisconsin Master Electrician
> BSEE
>
>
> On Wed, Oct 28, 2020 at 5:47 AM Christopher Warfel <
> [email protected]> wrote:
>
>> I would think that would be illegal.  They don't have jurisdiction on
>> supply side taps. It's past the meter, and expressly allowed in the NEC.  I
>> would definitely first ask to talk to a higher level person than the one
>> denying it (paper trail important). If that does not work, then the PSC is
>> your best option.  Chris
>> On 10/27/2020 6:27 PM, Kristopher Schmid wrote:
>>
>> Hi All,
>>
>> I have a utility that is hinting that they are going to deny my
>> interconnection application with a supply side connection and require a
>> load side.  Has anyone seen this before?
>>
>> (Proposed interconnection would be with Milbank step lugs in a 200 A
>> socket and a 60 A fused disconnect within 10 feet.)
>>
>> If they refuse it, i am thinking that registering a complaint with the
>> Wisconsin PSC may be appropriate.
>>
>> Kris
>>
>>
>> Shine On!
>>
>> Kris Schmid
>> Legacy Solar, LLC
>> 137 West 1st Avenue
>> Luck, WI 54853
>> www.legacysolar.com
>> 715-653-4295
>> NABCEP Certified PV Installation Professional
>> Licensed Wisconsin Master Electrician
>> BSEE
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & 
>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the 
>> other:https://www.mail-archive.com/[email protected]/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to