Hi Jason

My question is if it’s 200a in from the main breaker and 100a from PV its 300 
amps on the buss correct?

How is that ok with the 125% rule?  

Or is this covered by some other rule as it’s a feed through lug load center?

Jay



> On Nov 8, 2020, at 9:46 AM, Jason Szumlanski 
> <[email protected]> wrote:
> 
> 
> Maybe this is a better example (attached). I don't see how this would be a 
> problem under NEC 2014, 2017, or 2020. No portion of the main bus, feeder 
> conductors, or subpanel could possibly be subjected to overcurrent without an 
> OCPD stopping it.
> 
> My point is that here we are, 3 code cycles in since feeder taps were 
> addressed, and there is still no clarification of intent. AHJs are still 
> struggling with this. 
> 
> I'm not sure where residential meter/mains with feed through lugs are 
> popular. I know they are in Florida and I have heard Hawaii. I'm curious what 
> your jurisdictions think of this if you have this scenario. Most of the time 
> the subpanel is main lug only, but adding a main circuit breaker is usually 
> an easy and cost-effective fix to make this interconnection type work.
> 
> Jason Szumlanski
> 
> 
> 
> 
> 
>> On Wed, Oct 28, 2020 at 5:15 PM Jason Szumlanski 
>> <[email protected]> wrote:
>> For further discussion, I don't see how my original scenario is any 
>> different from this attached scenario, which I think everyone would agree is 
>> allowed. All conductors and busbars are subject to the same potential loads 
>> and fault currents. 
>>  (Image attached).
>> 
>> 
>> 
>>> On Wed, Oct 28, 2020 at 5:01 PM Jason Szumlanski 
>>> <[email protected]> wrote:
>>> Of course the feeder conductors and bus bar could be subjected to a fault. 
>>> But we're not talking about faults here. Fault protection is the job of the 
>>> PV OCPD And primary supply OCPD to protect the downstream busbar and 
>>> feeders. If that wasn't the case, you would need a new OCPD on BOTH the 
>>> load and line side of a solar connection as a feeder tap, not just the load 
>>> side.
>>> 
>>> If your interpretation is correct regarding the location of the OCPD, that 
>>> sounds like a sub-feed breaker is the only way to comply, and I haven't 
>>> seen such an animal for a typical residential load center. You can get 
>>> these for NQ panelboards and similar panelboards from other manufacturers 
>>> of course. It doesn't say as close as practicable or anything like that. It 
>>> says that a busbar connection is allowed when there are feeder CONDUCTORS 
>>> connected to feed through LUGS. What does "overcurrent device .. at the 
>>> supply end" mean? I emphasize "at." It's unclear how you would implement 
>>> this other than a sub-feed breaker I suppose, but that's not what it says. 
>>> It refers to feeder conductors on lugs on busbars, not feeder conductors on 
>>> load-side terminals of an overcurrent device.
>>> 
>>> My point is that 705.12 should have been wrapped up neatly in a bow, but 
>>> the lack of clarity, still, is astonishing. Why add a section about 
>>> feed-through lugs if it's going to be so vague?
>>> 
>>> Jason
>>> 
>>> 
>>> 
>>> 
>>>> On Wed, Oct 28, 2020 at 3:37 PM Brian Mehalic <[email protected]> 
>>>> wrote:
>>>> Hey Jason, 
>>>> Here's the 2020 text:
>>>> 
>>>> 6)  Connections shall be permitted on busbars of panelboards that supply 
>>>> lugs connected to feed-through conductors. The feed-through conductors 
>>>> shall be sized in accordance with 705.12(B)(1). Where an overcurrent 
>>>> device is installed at the supply end of the feed-through conductors, the 
>>>> busbar in the supplying panelboard shall be permitted to be sized in 
>>>> accordance with 705.12(B)⁠(3)⁠(1) through 705.12(B)(3)(3).
>>>> 
>>>> The OCPD on the supply end of the feed-through conductors would be in the 
>>>> form of a sub-feed breaker at the point of supply to those conductors, 
>>>> re-establishing overcurrent protection of the conductors (likely at the 
>>>> same ampacity as the main breaker in the supplying panel.  The 
>>>> feed-through conductors are basically an extension of the busbar in the 
>>>> supplying panel; they can either be protected by the main, or in the 
>>>> presence of multiple sources of power in the supplying panel (such as a 
>>>> backfed PV system breaker) they can be protected based on (B)(3)(1) - "the 
>>>> 125% rule" - or they can be protected by a new overcurrent device at their 
>>>> point of supply, in which case current on them is limited based on that 
>>>> OCPD size; in this latter scenario the busbar in the supplying panel is 
>>>> allowed to be sized based on one of (B)(3)(1) - (3) because it is 
>>>> protected downstream at its end.
>>>> 
>>>> The theory is pretty much the same as 705.12(B)(1) for feeders - when not 
>>>> connecting at the end of the feeder, use the "125% rule" or re-establish 
>>>> overcurrent protection for that portion of the feeder subject to multiple 
>>>> power sources.
>>>> 
>>>> In your drawing the 200 A feeder conductors, as well as the busbar below 
>>>> the PV system breaker, could be subject to > 200 A in the event of a fault 
>>>> somewhere along those conductors. 
>>>> 
>>>> Brian Mehalic 
>>>> NABCEP Certified Solar PV Installation Professional™ R031508-59
>>>> National Electrical Code® CMP-4 Member
>>>> (520) 204-6639
>>>> 
>>>> Solar Energy International
>>>> http://www.solarenergy.org
>>>> 
>>>> SEI Professional Services
>>>> http://www.seisolarpros.com
>>>> 
>>>> 
>>>> 
>>>>> On Wed, Oct 28, 2020 at 10:18 AM Jason Szumlanski 
>>>>> <[email protected]> wrote:
>>>>> Does anyone else think they botched the wording in this section? It's 
>>>>> still not clear, and we have a ton of meter/main combos with feed-through 
>>>>> lugs around here.
>>>>> 
>>>>> Where is it written, "where an overcurrent device is installed at the 
>>>>> supply end of the feed-through conductors," (emphasis added) are they 
>>>>> referring to the solar backfed breaker on the busbar or another breaker 
>>>>> somewhere along the feeder circuit? It goes on to state that the loads on 
>>>>> the supplying busbar can comply with any method in 705.12(B)(3), which 
>>>>> prescribes an OCPD at the load end of the feeder in 705.12(B)(3)(3), so 
>>>>> they can't be talking about that. I have to assume it is the solar 
>>>>> backfed breaker they are referencing.
>>>>> 
>>>>> See my interpretation of one scenario in the attached image. 
>>>>> 
>>>>> We're a long way off from the 2020 code implementation here, but it can 
>>>>> help sway plans examiners looking to clarify the intent of the 2014/2017 
>>>>> code cycles.
>>>>> 
>>>>> 
>>>>> Jason Szumlanski
> 
> <Feed Through Lug Interconnection Option (2).pdf>
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to