The Time of Use feature can support this request. I do understand that 
programming can be somewhat confusing in completely covering what you are 
wanting the generator can do. However, if you are wanting the generator to turn 
on only when the batteries are low and getting through the night then we can 
set the Time of Use to only turn on with specific  hours and also charge up to 
specific SOC. We implemented this setting so that there is the ability to 
control how much fuel is used and not run the gen for long periods of time. The 
Time of Use settings are very customizable, if you would like to give our 
support team a call and we can help customize it to best fit your scenario.



As for updating the system itself, we offer different avenues of doing so. The 
first is the Wi-fi dongle that is connected to the inverter and to the 
customers home network. We also offer different aftermarket versions for 
customers with specific needs or if they don't have internet altogether. There 
is a ethernet version for those that don't want the over the air (OTA) 
connection to there wireless network or possibly if there router itself is a 
little to far away from where the unit is located. Simply running a ethernet 
cable to this specific dongle will connect them for monitoring and also allow 
for updates. The final version is for those true off grid installs where they 
are not worried about monitoring but do need to get the system updated. We have 
developed a custom design dongle that once inserted into the unit will perform 
the update on the inverter locally. Plug it in and wait for the final part of 
the software to finish and now your system will have the current version of 
software. You can then remove it and adjust the settings for the new features 
that were added.


Thank you and have a blessed day,

Dustin Douglas

Sol Ark Engineering Support

(972) 575-8875 x 108

http://www.sol-ark.com/






---- On Fri, 13 Nov 2020 08:46:31 -0600 Jay <[email protected]> wrote ----



I’m wondering how the firmware is updated?  USB or other?  I’ve looked on the 
website but I couldn’t find any instructions. 



Thx

Jay







On Nov 12, 2020, at 7:58 PM, Jeff Clearwater 
<mailto:[email protected]> wrote:



  Thanks Dustin for keeping 
us up to date on Sol-Arks feature progress.

 

 While you are upgrading your firmware: :)

 

 So an essential feature for off-grid with a generator is to be able to 
program various SOC levels for generator start AND shuf-off after 
charge.  90% is way too high for many sunny climes and other 
configurations.  Often batteries need a boost in the wee morning hours -
 when they drop below the preferred recharge point but that's only 
perhaps a few hours before the sun comes up - So say you want to start a
 gen to charge a Lead-acid battery at 50% or an LFP batter at 20% SOC 
but you only want to bring it through to the next often or possibly 
sunny morning.  So you set it to run from 50% to 65% (or from 20%-40% 
for LFP) - knowing that the morning sun will take it the rest of the 
way.  90% would waste a ton of fuel in this scenario not too mention 
unwanted noise and wear and tear on the genny.  Depending on the clients
 use profile, the climate, and relative size of the array and battery 
and gen, these figures could vary anywhere from 20% to 100%.  So it's 
essential us off-grid installers have that flexibility.

 

 Also I know that your TOU settings might cover this (though not in all 
modes I believe) but another nice feature is to have 2 or 3 time periods
 with different start and stop settings (Sunny Island does this 
nicely).  So if the minimum SOC is reached in the evening you might as 
well bring it up to a higher SOC for gen shut down as it needs to get 
through the entire night whereas if that minimum SOC start trigger is 
met after 3 AM  it needs to only bring it to a lower SOC as described 
above.

 

 I'm loving the Sol-Ark product so far but it is obvious the
 software is a work in progress - the architecture and thought behind it
 is an excellent foundation - thanks for your work and openness for 
input to make it even better.

 

 Best,

 

 Jeff

 

 ~~~~~~~~~~~
  
Jeff Clearwater
 Village Power Design
 https://www.linkedin.com/in/jeff-clearwater-0622a312/ 
 http://www.villagepowerdesign.com
 cell - 413-559-9763
 ~~~~~~~~~~~~~~~~~~~~~~~






mailto:[email protected]

November
 12, 2020 at 11:46 AM



Hi All,



First and foremost 
thank you for sharing your experiences the the Sol-Ark system. We try 
very hard to have different capabilities and add new features that make 
it flexible for the customer. The two-wire start is a feature however 
that we want to be seamless. In the instance where the customer is 
seeing the system shutdown once the generator shuts off has been 
addressed and fixed with a software update. With this update we are able
 to handle larger generators that tend to drift from 60hz. Please give 
our support team a call so that we can update the customer accordingly. 
We are also looking at adding more features including the ability 
exercise the generator in the near feature. 



Thank 
you and have a blessed day,

Dustin
 Douglas

Sol Ark Engineering Support

(972) 575-8875 x 108

http://www.sol-ark.com/






---- On Thu, 12 Nov 2020 08:08:51 -0600 Jay mailto:[email protected] wrote 
----









_______________________________________________
List sponsored 
by Redwood Alliance

List Address: mailto:[email protected]

Change
 listserver email address
 & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There
 are two list archives for searching. When one doesn't work, try the 
other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List
 rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check
 out or update participant bios:
http://www.members.re-wrenches.org



mailto:[email protected]

November
 12, 2020 at 9:08 AM



Hi Bill



In the 
past I’ve had similar issues with generators/inverters. Usually a relay 
on the output power wires that opens( disconnects) when the stop signal 
is sent works as the frequency doesn’t slowly go down, it drops to 0 
instantly. 

I don’t know if it will fix your issue. 



Seems like solark needs to greatly 
improve their firmware. 



Jay



Peltz power. 















_______________________________________________
List
 sponsored by Redwood Alliance

List Address: mailto:[email protected]

Change
 listserver email address
 & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There
 are two list archives for searching. When one doesn't work, try the 
other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List
 rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check
 out or update participant bios:
http://www.members.re-wrenches.org



mailto:[email protected]

November
 11, 2020 at 10:03 PM



Hi folks--We've also been disappointed with the 
Sol-Ark two-wire generator start. The unit starts at the charge set 
point, but the inverter will shut down for about a minute every time the
 generator stops running. After the minute wait, the inverter restarts 
and everything is fine. But it is aggravating for the homeowners to be 
left wondering in the dark.



Sol-Ark says that when the generator 
shuts off, the frequency drops out of the Sol-Ark range and causes the 
inverter shut down. 

They 
suggested we find a way to increase the generator speed to avoid the 
frequency drop at shutdown. This seems like a lame suggestion, since the
 generator has no idea of when the batteries will be satisfied--it only 
responds to the on/off signal from the Sol-Ark. I would think that the 
unit could be programmed to ignore the frequency drop when it sends the 
shut off signal to the generator. The system has an an Ecogen 
15kW.



Not having an exercise function is also a
 miss. As mentioned below, the time of use can be used, but one has to 
go out and play with the programming to check the generator.



regards, bill



Bill
 Hennessy
Berks Solar, LLC
371 Centennial Rd
Mertztown, PA 
19539

o 610 682 4300
c 484 560 4666
NABCEP certified 
installer
PA contractor #44411
http://www.berkssolar.com







On Wednesday, November 11, 2020, 8:20:57 PM EST, 
Chris Sparadeo mailto:[email protected] wrote:





Thanks for the suggestion, Jay. 



Yes,
 the Sol-Ark has a very basic and limited AGS for 2 wire compatible gen 
sets. Gen start can be programmed with voltage or SOC, however gen stop 
is not a function that can not be readily programmed. Instead, the 
Sol-Ark is programmed to charge the battery bank to 90% of  the rated Ah
 capacity of the battery bank before turning off the generator. You can 
ultimately adjust this gen stop parameter to be based on a specific SOC 
or voltage, but I believe that doing so requires a call into tech 
support. The tech I spoke with updated a setting (having to do with 
a TOU parameter I believe) that was not accessible via the system 
interface. AGS  from Schnieder, Outback and even Magnum are less clunky,
 but I am hoping that Sol-Ark will eventually come out with new 
programming to remediate these minor but nevertheless, important issues




-Chris




On Wed, Nov 11, 
2020 at 3:58 PM Jay <mailto:[email protected]> wrote:







-- 

Chris 
Sparadeo





C_802-369-4458

H_802-728-3059








_______________________________________________
List sponsored by Redwood Alliance

List Address: mailto:[email protected]

Change listserver email address & 
settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for 
searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org









_______________________________________________
List
 sponsored by Redwood Alliance

List Address: mailto:[email protected]

Change
 listserver email address
 & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There
 are two list archives for searching. When one doesn't work, try the 
other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List
 rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check
 out or update participant bios:
http://www.members.re-wrenches.org






_______________________________________________

List sponsored by Redwood Alliance



List Address: mailto:[email protected]



Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



There are two list archives for searching. When one doesn't work, try the other:

https://www.mail-archive.com/[email protected]/

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

http://www.re-wrenches.org/etiquette.htm



Check out or update participant bios:

http://www.members.re-wrenches.org






_______________________________________________ 

List sponsored by Redwood Alliance 

 

List Address: [email protected] 

 

Change listserver email address & settings: 

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

 

There are two list archives for searching. When one doesn't work, try the 
other: 

https://www.mail-archive.com/[email protected]/ 

http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 

 

List rules & etiquette: 

http://www.re-wrenches.org/etiquette.htm 

 

Check out or update participant bios: 

http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to