Fellow Wrenches,

I don't often use Exeltech inverters, as they're not designed for common whole-house applications, lacking a generator charging function. But sometimes a small system is a good match for their clean waveform. For years their XP line was a decent choice for a tiny house or similar small-loads system. For a recent budget system for a yurt, I had rejected the XP line, as I thought that at 1,100 watts AC out the XP1100 was their largest offering and it was too small for a couple of loads. I learned, though, that Exeltech now makes a 2,000 watt model. I ordered one directly from Exeltech for this job.

It works, but has a fundamental design limitation severe enough to be of limited usefulness in most remote home applications, especially in colder winter climates. I'm writing this as a heads-up to others. The limitation is simply this: DC voltage to the unit is capped at 30V DC, and above this voltage the unit shuts off until the battery voltage is reduced. This limits the unit pretty much to VRLA or lithium batteries (no equalizing) and warmer climates or indoor locations.

The smaller XP600 and 1100 have a HVD of 16.5/33/66 VDC, so this isn't an issue with these units. The 2 kW units are rated 15/30/60 VDC, and this is nonadjustable. There are no warnings on the spec sheet or in the manual about this limitation.

Allan

--

*Allan Sindelar*
[email protected] <mailto:[email protected]>
NABCEP Certified PV Installation Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to