Hi Jason

I’ve seen this happen to battleborn. 
They sell a totally cobbled part to prevent that. 

Jay


> On Jan 31, 2021, at 3:35 PM, Jason Szumlanski 
> <[email protected]> wrote:
> 
> 
> I had another battery manufacturer's BMS contactor weld shut due to an inrush 
> current problem with another brand of inverter. That was "fun." It seems 
> strange that this issue of cap loading hasn't been addressed. Hopefully it 
> will be. 
> 
> To clarify the SOC not drifting... Are you saying in an off-grid system you 
> can reliably use the Sol-Ark SOC to trigger generator start and charging 
> parameters without causing discrepancies in SOC on the battery meter itself 
> and balancing is not a problem? If so, I'm comfortable with that I think. 
> 
> Jason
> 
> 
> 
> 
>> On Sun, Jan 31, 2021, 3:45 PM Jeff Clearwater <[email protected]> 
>> wrote:
>> Hey Jason,
>> 
>> I've installed a few systems now using Fortress eVaults.  I like them as 
>> they are a nice 18.5 KW increment and the BMS seems hardy - nice interface 
>> screen showing SOC on each battery.
>> 
>> However, call Fortress and discuss the status of their closed loop 
>> communications (and talk to Sol-Ark about it too).  The tech at Fortress 
>> told me that less than 4 eVaults the closed loop communication is more 
>> trouble than it's worth between batteries.  That appears to be because they 
>> simply have not employed a soft-start resistor and the batteries shut down 
>> when exposed to cap loading during inverter start-up.  They said relying on 
>> the individual battery BMSs works fine.  I've found that to be true so far - 
>> no drift in SOC from battery and Sol-Ark.
>> 
>> Their eFlex system is supposed to be totally closed loop communication 
>> between batts and with a Sol-Ark.  It's a bit of a small increment for large 
>> systems but may be worth it.
>> 
>> I imagine they will offer an upgrade for eVaults or a new model soon with 
>> full closed loop.  Sol-Ark tech said they were still working with them on 
>> that.
>> 
>> Hope that helps!
>> 
>> Best,
>> 
>> Jeff
>> 
>>> Jason Szumlanski January 31, 2021 at 11:27 AM
>>> I'm seeing a lot of pictures of LiPO battery systems and people are 
>>> mounting equipment above them like load centers, inverters with 
>>> disconnects, and other serviceable enclosures. Some of these battery 
>>> systems are 24 inches deep or more. This seems to violate NEC 110.26 
>>> requirements for the other serviceable equipment, but the pictures are 
>>> proudly displayed as models of success. Even slender Tesla Powerwalls stick 
>>> out significantly when stacked 2 or 3 deep and would be more than 6 inches 
>>> deeper than a standard load center. Sure, the battery cabinets make great 
>>> places to rest tools while working, but does anyone else see this as 
>>> problematic? 
>>> 
>>> Jason Szumlanski
>>> Florida Solar Design Group 
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected]
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>> 
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to