Hello Kirpal
Hello Wrenches
This can be accomplished using the Mate3(s) and Flextime.
Flextime allows up to 3 modes in a 24 hour day.
Flextime uses a 24 hour clock to instruct a system to switch modes based on 
time.
A good knowledge of the modes and how they work is helpful.
Results may vary depending on solar vs loads.
Below is a picture of a system set up to achieve your request.
Adjust the times to suit your individual needs.
The setting below are as follows
1800 to 1830 Grid Tied and sell enabled
1830 to 0700 Grid Zero (no sell and no  charge from the grid)
0700 to 1800 Back Up (allowing the unit to pass through and charge)
 Again a good knowledge of how the modes function and the charging triggers 
(Re-Bulk and Re-Float) is helpful.
One of the advantages is this can be done via optics so fine tuning can be 
accomplished by
monitoring the system over time as it goes through the various sequences.


[cid:[email protected]]
I hope this helps.
Take Care All



From: RE-wrenches <[email protected]> On Behalf Of 
Kirpal
Sent: Thursday, February 4, 2021 8:22 AM
To: RE-wrenches <[email protected]>
Subject: [RE-wrenches] grid sell back time settings on Outback systems

Hi Folks....
We have a scenario where we would like to control when our system sells power 
back to the grid.  Basically, we only want to sell back while the sun is 
shining. We would like to stop selling based on programmed clock settings.  I 
know in HBX mode we can control when we buy from the grid, wondering if anyone 
knows how to control if and when we sell to the grid, separate from voltage set 
points.  In this situation we basically don't want to sell hydro power back at 
night.
We can create our own relay controls to prevent if we need to, but hoping 
someone has a Mate controller based programming solution.  I can't seem to find 
it and at first glance Outback tech support didn't have an answer...It was a 
new tech support guy I spoke with and he was going to do some research and get 
back to me.
100 Thanks!

Sunny Regards,
Kirpal Khalsa
Oregon LRT#25
Oregon Solarworks LLC
www.oregonsolarworks.com<https://protect2.fireeye.com/v1/url?k=49430a66-16d832a0-494003ed-8656ebba2f0b-766b497cb6918bea&q=1&e=76ee1199-0f8b-49d3-a655-327a42c2fc49&u=http%3A%2F%2Fwww.oregonsolarworks.com%2F>
541-299-0402


This email and any attachments may contain confidential information that is 
intended only for the recipient(s). If you have received this email in error, 
please notify the sender and delete it from your system. Any views or opinions 
presented in this email are solely those of the author and do not necessarily 
represent those of the company or its affiliates. This email does not 
constitute an agreement to conduct transactions by electronic means and does 
not create any legally binding contract or enforceable obligation in the 
absence of a fully signed written contract. The recipient should check this 
email and any attachments for viruses. The company accepts no liability for any 
loss or damage caused by software viruses. If you are the intended recipient 
and you do not wish to receive similar email(s) from us in the future then 
please notify the sender. Please consider the environment before printing.
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to