> The main reason the manual instructs not to top up all cells before 
> equalizing is to avoid overfilling to/up in the vent and having a spillover 
> when they bubble. 
> 
> We suggest inspecting and topping them up after because they also go through 
> water running the equalization. If a cell is noticeably lower than others it 
> would make sense to top it up slightly to bring the electrolyte to a similar 
> level as the others before beginning the process.  If it's just one cell in 
> the bank I would expect the SG reading on that one will be off from the 
> others to begin with. If it's going through more water than others it's 
> getting hotter.  Why?
> 
> Lower liquid level doesn't always equate to higher acid concentration. The SG 
> reading in the cell with lower electrolyte would only read higher than others 
> if the cell, like the others, wasn't suflated.  If it is sulfated, the SG 
> readings at full charge are lower because the sulfate has accumulated on the 
> plate and not released back into the electrolyte during charging.
> 
> First, he should check all cells at float charge before beginning the 
> equalization so he knows where they're all starting from. Is the cell with 
> the lower electrolyte level reading higher or lower SG than the others?  Are 
> the rest completely balanced and this one is off?
> 
> SG readings immediately after equalization and before adding water will be 
> elevated due to temperature. To get accurate readings after adding water he 
> should cycle the batteries 2-3 times, allowing it to mix normally, and then 
> check SG at float charge. SG results after an equalization are accurate after 
> the bank has been cycled a few times. If cell(s) were sulfated, they will 
> continue to desulfate as they're cycled normally so the results aren't 
> immediate.
> 
> 
> 
> 
> 
> 
> 
> 
>  <http://www.rollsbattery.com/> <http://www.rollsbattery.com/> 
> <http://www.rollsbattery.com/> <http://www.rollsbattery.com/> 
> <http://www.rollsbattery.com/> <http://www.rollsbattery.com/> 
> <http://www.rollsbattery.com/> <http://www.rollsbattery.com/> 
> <http://www.rollsbattery.com/> <http://www.rollsbattery.com/> 
> <http://www.rollsbattery.com/> <http://www.rollsbattery.com/> 
> <http://www.rollsbattery.com/> <http://www.rollsbattery.com/> 
> <http://www.rollsbattery.com/> <http://www.rollsbattery.com/> 
> <http://www.rollsbattery.com/> <http://www.rollsbattery.com/> 
> <http://www.rollsbattery.com/> <http://www.rollsbattery.com/> 
> <http://www.rollsbattery.com/>Jeff Myles ⋅ Marketing Manager
> t +1.902.597.4012 m +1.902.802.6962
> f +1.902.597.8447 e [email protected] <mailto:[email protected]>
> international mobile +1.917.463.8389
>  <x-msg://45/#SignatureSanitizer_SafeHtmlFilter_> 
> <http://www.facebook.com/RollsBattery> <http://www.facebook.com/RollsBattery> 
>  <> <http://www.twitter.com/RollsBattery>  <> 
> <https://www.youtube.com/user/RollsBattery>  <> 
> <https://www.linkedin.com/company/rolls-battery-engineering> <> 
> <http://www.instagram.com/RollsBattery> 
> <http://www.instagram.com/RollsBattery> 
> <http://www.instagram.com/RollsBattery>
> CONFIDENTIALITY: The information transmitted herein is intended only for the 
> addressee and may contain confidential, proprietary and/or privileged 
> material. Any unauthorized review, distribution or other use of or the taking 
> of any action in reliance upon this information is prohibited. If you receive 
> this email in error, please contact the sender and delete or destroy this 
> message and all copies.
> 
> 
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to