Jason,

We recently completed a ground-mount array ~350’ from the Envoy and all micros 
are able to report. 


> On Mar 1, 2021, at 8:47 AM, Jason Szumlanski 
> <[email protected]> wrote:
> 
> How far has anyone ever put an IQ Envoy from an array and successfully 
> monitored it?
> 
> I am planning a ground mount that is 300 feet from a home with 12/240V 
> service. The branch circuits will have an AC combiner panel on a rack at the 
> array with 2 parallel sets of 4/0 Al conductors back to the interconnection 
> point at the house in a meter/main combo. I was planning to put a breaker in 
> the meter/main combo for the IQ Envoy inside an adjacent enclosure. I'm 
> wondering if I will be successful in picking up the microinverters 300 feet 
> away. 
> 
> I'd rather do this than locate that IQ Envoy near the array and worry about 
> getting Internet out there. I know Cellular is an option, but I hate the 
> 6-hour delay in data acquisition.
> 
> Thanks,
> 
> Jason Szumlanski
> Florida Solar Design Group
> 
> 
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergy.com
Check, Virginia 24072
Office: 540.235.3095
Mobile: 540.808.9502

VA Class A Contractor Lic# 2705147660
VA Master Electrician Lic# 2710062762
VA Alternative Energy Systems Installer  
NABCEP Certified PV Installation Professional 110112-21



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to