The Radian is also the system that I would typically use in this situation.
Although I am interested what people think about using a Sol-Ark inverter
here. I have not used one yet, but I am interested in the fact that
everything is integrated into one box, the string voltages can be up to
500V, and also if there is a battery failure at some point they can still
run as a grid tied system.
Cheers,
Dave

*Dave Tedeyan, PE*
Senior Engineer | Taitem Engineering, PC

110 South Albany Street | Ithaca, NY 14850
o. *607.277.1118 x121*  f. 607.277.2119
www.taitem.com

Solar • Sustainability • Energy • Design
Certified B-Corporation since 2013


On Wed, Mar 3, 2021 at 7:10 AM John Blittersdorf <
john.blittersd...@gmail.com> wrote:

> William,
>    I agree with you with Radian, Fortress and just add a subpanel
> identical to the main grid panel as close possible. Put all critical loads
> on sub and larger loads on grid panel.  Being side by side, swapping
> circuits is easy. I also install an iota charger for generator redundancy.
> OpticRE works great for monitoring.
>
> John Blittersdorf
>
> On Wed, Mar 3, 2021 at 1:19 AM William Miller <will...@millersolar.com>
> wrote:
>
>> Friends:
>>
>>
>>
>> I am getting asked more often to provide design for grid-tied battery
>> backup systems.  I generally try to talk clients out of battery backup
>> because I have always felt that the grid is the greenest battery and that
>> the grid reliability is better than one might remember.  However, with
>> climate change and media attention, the need and market pressure is
>> becoming stronger.
>>
>>
>>
>> I am really interested in what others have created in the way of
>> solutions to this question.  I have thought about it a lot.  If its ok, I’d
>> like to free-associate about some of my concerns and conclusions then ask
>> if any of you are willing to share your ideas on how best to fill this
>> need.  Here goes:
>>
>>
>>
>> I am a firm believer in segregate load delivery for these reasons:
>>
>> 1.   To back up an entire grid service you have to, in good conscience,
>> perform a thorough load study and provide enough through-transfer to
>> provide for maximum load conditions during grid up-time.  The backup system
>> cannot be a supply bottle-neck.
>>
>> 2.   I don’t accept manual load-shedding for one moment.  What if the AC
>> and the dryer are running when the grid goes out?  The system crashes.
>>
>> 3.   In a home with whole-house backup, it is difficult for the consumer
>> to know there is an outage and to conserve.  Cellphone notification
>> features are now more common, but cell phone batteries die and phones get
>> left in the other room with the ringer off, so it is possible for
>> homeowners to leave consumptive loads on after the grid goes down.
>>
>>
>>
>> Conclusion:  With segregated loads, the transfer, inverter and storage
>> can be scaled down and the reliability increases.  Less cost, better
>> performance.
>>
>>
>>
>> So given that the system sizing will be modest, has anyone come up with a
>> reasonable design using standard, grid-sell capable battery inverters?
>>
>>
>>
>> Here is how I am imagining such a system:
>>
>>
>>
>> I see a modest battery system with a 4 to 8 KW inverter, DC coupled PV
>> and a matching no-maintenance battery system. It would have these
>> components:
>>
>>
>>
>> Inverter:  Must have a dedicated generator and grid input and good remote
>> monitoring,  robust web interface and email notification.  Outback Radian.
>>
>>
>>
>> Batteries:  Gel or lithium.  I have a client that has been grid-floating
>> a set of MK Powered gel batteries since 1999.  Or a Blue Planet or Fortress
>> cabineted system.
>>
>>
>>
>> Generator:  Small pad-mount natural gas or propane fueled generator or a
>> portable gas powered unit with stabilized gas.  If the generator is
>> portable, provide an AC flanged inlet and sturdy cord long enough so
>> generator can be 10 feet from any opening in the home.  Provide durable
>> signage on the generator indicating CO safety practices.
>>
>>
>>
>> PV: DC coupled for simplicity.  Sized based on annual energy needs, not
>> on critical loads.  Grid power is likely to go down in the stormy winter
>> months or smoky fire season, so PV is not a reliable energy source during
>> grid outages.
>>
>>
>>
>> AC Distribution:  Segregated loads with at least one commonly used
>> lighting circuit not on the critical loads panel so the homeowner soon
>> realizes the power is out.
>>
>>
>>
>> Unless you are a Tesla dealer, I am sure many of you have gone through
>> the same mental acrobatics trying to figure out the best solution to this
>> design request.  I am very interested in what the rest of you may have come
>> up with.
>>
>>
>>
>> Thanks in advance.
>>
>>
>>
>> William Miller
>>
>>
>>
>> Miller Solar
>>
>> 17395 Oak Road, Atascadero, CA 93422
>> <https://www.google.com/maps/search/17395+Oak+Road,+Atascadero,+CA+93422?entry=gmail&source=g>
>>
>> 805-438-5600
>>
>> www.millersolar.com
>>
>> CA Lic. 773985
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to