Good morning all. We have installed numerous Sol-Arks for this type of 
application over the last 2 years and they perform so very well. While they do 
a great job with FLA’s they really shine with LI’s or maybe it is my bias about 
only having to install 1 or 2 large batteries. Technology has blessed us with 
great changes in our industry and like some of you, I, at times, have been 
reluctant to change. Sol-Ark , while a truly terrific product, will be copied 
by competitors and upstarts, providing us with additional options in the 
future, good bad or indifferent.  We and our customers will benefit, here’s to 
change.



Peter Giroux

American Solar

Roswell Ga



From: RE-wrenches <[email protected]> On Behalf Of Dave 
Tedeyan
Sent: Wednesday, March 3, 2021 8:30 AM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Small, non-Tesla GTBB system design



The Radian is also the system that I would typically use in this situation. 
Although I am interested what people think about using a Sol-Ark inverter here. 
I have not used one yet, but I am interested in the fact that everything is 
integrated into one box, the string voltages can be up to 500V, and also if 
there is a battery failure at some point they can still run as a grid tied 
system.

Cheers,

Dave




Dave Tedeyan, PE

Senior Engineer | Taitem Engineering, PC



110 South Albany Street | Ithaca, NY 14850

o. 607.277.1118 x121  f. 607.277.2119

www.taitem.com <http://www.taitem.com>



Solar • Sustainability • Energy • Design

Certified B-Corporation since 2013





On Wed, Mar 3, 2021 at 7:10 AM John Blittersdorf <[email protected] 
<mailto:[email protected]> > wrote:

William,

   I agree with you with Radian, Fortress and just add a subpanel identical to 
the main grid panel as close possible. Put all critical loads on sub and larger 
loads on grid panel.  Being side by side, swapping circuits is easy. I also 
install an iota charger for generator redundancy. OpticRE works great for 
monitoring.



John Blittersdorf



On Wed, Mar 3, 2021 at 1:19 AM William Miller <[email protected] 
<mailto:[email protected]> > wrote:

Friends:



I am getting asked more often to provide design for grid-tied battery backup 
systems.  I generally try to talk clients out of battery backup because I have 
always felt that the grid is the greenest battery and that the grid reliability 
is better than one might remember.  However, with climate change and media 
attention, the need and market pressure is becoming stronger.



I am really interested in what others have created in the way of solutions to 
this question.  I have thought about it a lot.  If its ok, I’d like to 
free-associate about some of my concerns and conclusions then ask if any of you 
are willing to share your ideas on how best to fill this need.  Here goes:



I am a firm believer in segregate load delivery for these reasons:

1.   To back up an entire grid service you have to, in good conscience, perform 
a thorough load study and provide enough through-transfer to provide for 
maximum load conditions during grid up-time.  The backup system cannot be a 
supply bottle-neck.

2.   I don’t accept manual load-shedding for one moment.  What if the AC and 
the dryer are running when the grid goes out?  The system crashes.

3.   In a home with whole-house backup, it is difficult for the consumer to 
know there is an outage and to conserve.  Cellphone notification features are 
now more common, but cell phone batteries die and phones get left in the other 
room with the ringer off, so it is possible for homeowners to leave consumptive 
loads on after the grid goes down.



Conclusion:  With segregated loads, the transfer, inverter and storage can be 
scaled down and the reliability increases.  Less cost, better performance.



So given that the system sizing will be modest, has anyone come up with a 
reasonable design using standard, grid-sell capable battery inverters?



Here is how I am imagining such a system:



I see a modest battery system with a 4 to 8 KW inverter, DC coupled PV and a 
matching no-maintenance battery system. It would have these components:



Inverter:  Must have a dedicated generator and grid input and good remote 
monitoring,  robust web interface and email notification.  Outback Radian.



Batteries:  Gel or lithium.  I have a client that has been grid-floating a set 
of MK Powered gel batteries since 1999.  Or a Blue Planet or Fortress cabineted 
system.



Generator:  Small pad-mount natural gas or propane fueled generator or a 
portable gas powered unit with stabilized gas.  If the generator is portable, 
provide an AC flanged inlet and sturdy cord long enough so generator can be 10 
feet from any opening in the home.  Provide durable signage on the generator 
indicating CO safety practices.



PV: DC coupled for simplicity.  Sized based on annual energy needs, not on 
critical loads.  Grid power is likely to go down in the stormy winter months or 
smoky fire season, so PV is not a reliable energy source during grid outages.



AC Distribution:  Segregated loads with at least one commonly used lighting 
circuit not on the critical loads panel so the homeowner soon realizes the 
power is out.



Unless you are a Tesla dealer, I am sure many of you have gone through the same 
mental acrobatics trying to figure out the best solution to this design 
request.  I am very interested in what the rest of you may have come up with.



Thanks in advance.



William Miller



Miller Solar

17395 Oak Road, Atascadero, CA 93422 
<https://www.google.com/maps/search/17395+Oak+Road,+Atascadero,+CA+93422?entry=gmail&source=g>

805-438-5600

www.millersolar.com <http://www.millersolar.com/>

CA Lic. 773985





_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected] 
<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



--
This email has been checked for viruses by AVG.
https://www.avg.com
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to