Come to VT... No inspection needed for residential solar installations at all 
(in the majority of the state). Having done hundreds of inspections for NYS, I 
can tell you that quality and code compliance race for the bottom dollar the 
majority of the time.Having been called upon to troubleshoot or expand others 
systems, it is the wild west.-GlennSent from my 'smart'phone, so please excuse 
typos and spelling errors.------ Original message------From: William 
MillerDate: Wed, Mar 31, 2021 1:37 PMTo: RE-wrenches;Cc: Subject:[RE-wrenches] 
Odd inspection procedureFriends: We just finished a grid-tied project that 
included a pretty complicated service upgrade.  The project is in Monterey 
County, California.  The site is pretty remote on the south end of the Big Sur 
coastline and Highway 1 is closed (as is not uncommon) to the north with a 
washout.  This makes it time consuming for an inspector to reach the site, but 
even without the washout the travel time is measured in hours. Days in
 advance we scheduled the final inspection on the building department web-site 
as is SOP and were awarded a slot for yesterday.  Yesterday morning an 
inspector called at 7:30 AM to announce they were too busy to make the 
appointment.  Instead I was directed to take a series of photographs to verify 
the validity of our installation work.  Below is the list they provided.  Note 
how vague the requirements are, particularly the fifth one.  I was told that 
this process will be standard operation procedure for the County of Monterey in 
the near future for solar installs.   This seems wrong to me.  I can’t believe 
that any collection of photographs can accurately portray if even the most 
simple photovoltaic system, let alone one with a 300 amp CT service and 400 amp 
transfer switch, is installed correctly.  I know in the 1980s the solar water 
heating industry had acquired a collective black-eye due to shoddy installation 
procedures and I fear this is where the PV industry may be 
 headed.   I
 submitted a handful of photos and was granted a final approval.  I have very 
mixed feelings about this “success.”  I feel like I cheated on a test.   I am 
curious if any of you have had a similar experience to this.  As always I am 
informed and sometimes amused by what I learn on this forum. List of requested 
photographs: ☐ PV module model number, quantity, and location according to the 
approved plan.  ☐ Roof penetrations flashed/sealed according to the approved 
plan.  ☐ Array exposed cables are properly secured, supported, and routed to 
prevent physical damage.  ☐ Grounding/bonding of rack and modules according to 
the manufacturer’s installation instructions.  ☐ Equipment installed, listed 
and labeled according to the approved plan (e.g., PV   modules, dc/dc 
converters, combiners, inverters, rapid shutdown equipment).  ☐ Overcurrent 
devices are the type and size according to the approved plan.  ☐ Disconnects 
according to the approved plan and prop
 erly located as required by the 
 NEC.  ☐ PV system markings, labels and signs according to the approved plan.  
☐ Connection of the PV system to the grounding electrode system according to 
the approved plan.  ☐ Access and working space for operation and maintenance of 
PV equipment such as  inverters, disconnecting means and panelboards (not 
required for PV modules) [NEC 110.26].  ☐ The rapid shutdown system is 
installed and operational according to the approved  plan [NEC 690.12].  
William Miller Miller Solar17395 Oak Road, Atascadero, CA 
93422805-438-5600www.millersolar.comCA Lic. 773985  
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to