Jay:

The back story is sometimes useful. Thank you for filling in the details.  

I have a soft spot for community radio. I also have some used, working SB 2500U 
inverters on the shelf.  I’d be happy to send you one. Contact me off  list.

The used inverter offered came from an art-house theater. These were the units 
I ordered for 208 by mistake and had to send back to be made 240. They were 
replaced by TL-21 inverters.   See this link if you are curious.

https://www.thepalmtheatre.com/about-us

I agree that in most cases we need to comply with updated standards. I have on 
occasion bent the rules to apply an in-stock inverter that does not meet the 
latest and greatest requirements to replace an older unit. For example I am 
pretty lenient with clients that want to remove an antiquated AES1000 or other 
inverter and put in something newer without stirring the hornets-nest of 
utility or building department approval.

William Miller
www.millersolar.com

> On May 18, 2021, at 7:15 PM, Jay <[email protected]> wrote:
> 
> 
> Dear wrenches
> 
> I did not include the back story as it is not relevant to my inquiry. However 
> given the comments I decided to include it in that it will hopefully clear up 
> any confusion. 
> 
> Where I used to live, the local community radio station ( poorly funded) has 
> a old PV system with you guessed it a SMA SB2500U that was installed brand 
> new a long time ago. 
> It failed and a replacement was located for $150.  But it was 208 and not 
> 240vac, which someone didn’t catch when ordering it. 
> A buck/boost transformer allows it to work but adds tare losses that we were 
> trying to remove. 
> 
> It is my understanding that a like for like component swap is covered under 
> code rules. Regardless, no inspection or calls to the county permit office 
> were made or will be made. One of the great joys of living very rurally. 
> 
> Back to my original post about how to or if it’s possible to convert a 208 to 
> 240vac SMA SB2500U, which appears to be no, thanks to all who contacted me. 
> 
> Jay
> 
> Peltz Power. 
> 
>>> On May 18, 2021, at 7:23 PM, Jerry Shafer <[email protected]> wrote:
>>> 
>> 
>> Wrenches
>> I would also be surprised if the old 2500 would last very long.
>> Better off with a SB5.0-41 and if you need RSD then add that in also.
>> 
>>> On Tue, May 18, 2021, 12:15 PM Dave Angelini Offgrid Solar 
>>> <[email protected]> wrote:
>>> Probably if it is old it does not have these recent Certifications and UL 
>>> requirements. Just gave these to my local AHJ.
>>> 
>>> IEEE 1547, UL 1741-SA, Rule 21, Rule 14H, PREPA, and CSA 107.1
>>> 
>>> Product Certification History Project Date Description 80049402 2020-09-18 
>>> Update to report 70194014 to meet grid support function according to CA 
>>> Rule 21 for 120Vac output configuration. 80036281 2020-03-15 Update report 
>>> 70194014 to include UL1741 CRD SA17/18 UL 1741(California Rule 21 Phase 3 
>>> Function 2 and Function 3) for Model XW Pro 6848 NA. 80020062 2019-10-30 
>>> Update report 70194014 to include firmware upgrade for Model XW Pro 6848 
>>> NA. 70220117 2019-03-27 Update Report 70194014 to include minor firmware 
>>> update for Model XW Pro 6848 NA. 70212688 2019-03-04 Update Report 70194014 
>>> to Include Volt-Watt and revised Freq-Watt grid tie requirements as per 
>>> UL1741 Supplement SA for Model XW Pro 6848 NA (FGA 865-6848-21).
>>> 
>>> Dave Angelini Offgrid Solar
>>> "we go where powerlines don't"
>>> http://members.sti.net/offgridsolar/
>>> e-mail  [email protected]
>>> text 209 813 0060
>>>> On Tue, 18 May 2021 14:07:08 -0400, "Glenn Burt" <[email protected]> 
>>>> wrote:
>>>> 
>>>> Hi Kirk,
>>>> 
>>>>  
>>>> 
>>>> Can you elaborate on which UL standards the older SB units don't comply 
>>>> with?
>>>> 
>>>>  
>>>> 
>>>> -Glenn
>>>> 
>>>>  
>>>> 
>>>> From: RE-wrenches <[email protected]> On Behalf Of 
>>>> Kirk Herander, VSE
>>>> Sent: Tuesday, May 18, 2021 6:42 AM
>>>> To: [email protected]
>>>> Subject: Re: [RE-wrenches] SMA SB 2500U
>>>> 
>>>>  
>>>> 
>>>> These older Sunnyboys do not comply with latest UL standards regardless. 
>>>> If its a new installation, a savvy utility  / AHJ will catch this.
>>>> 
>>>>  
>>>> 
>>>> Kirk Herander / [email protected]
>>>> 
>>>> Owner|Principal, VT Solar, LLC
>>>> 
>>>> Celebrating our 30th Anniversary 1991-2021!!
>>>> 
>>>> www.vermont.solar
>>>> 
>>>> dba Vermont Solar Engineering
>>>> 
>>>> 802.863.1202
>>>> 
>>>> On 5/17/2021 3:53:26 PM, William Miller <[email protected]> wrote:
>>>> 
>>>> Jay: 
>>>> 
>>>> Some years ago I mis-ordered 5 SB2500s for 208 three phase and it turned 
>>>> out the system was 240 VAC three phase (open delta). I had to return the 
>>>> inverters to the factory to be converted and I had to rewire all of the 
>>>> arrays. So no, I don't think this can be done in the field. 
>>>> 
>>>> William Miller 
>>>> 
>>>> Miller Solar 
>>>> 17395 Oak Road, Atascadero, CA 93422 
>>>> 805-438-5600 
>>>> www.millersolar.com 
>>>> CA Lic. 773985 
>>>> 
>>>> 
>>>> -----Original Message----- 
>>>> From: RE-wrenches [mailto:[email protected]] On 
>>>> Behalf Of Jay 
>>>> Sent: Monday, May 17, 2021 11:44 AM 
>>>> To: RE-wrenches 
>>>> Subject: [RE-wrenches] SMA SB 2500U 
>>>> 
>>>> Does anyone know if you can convert a 
>>>> SMA SB2500U ( old red inverter) from 208 to 240vac? 
>>>> 
>>>> Without using a boost transformer. 
>>>> 
>>>> Thx 
>>>> Jay 
>>>> 
>>>> Peltz power. 
>>>> 
>>>> 
>>>> _______________________________________________ 
>>>> List sponsored by Redwood Alliance 
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> 
>>>> List Address: [email protected] 
>>>> 
>>>> Change listserver email address & settings: 
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other: 
>>>> https://www.mail-archive.com/[email protected]/ 
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>> 
>>>> List rules & etiquette: 
>>>> http://www.re-wrenches.org/etiquette.htm 
>>>> 
>>>> Check out or update participant bios: 
>>>> http://www.members.re-wrenches.org 
>>>> _______________________________________________ 
>>>> List sponsored by Redwood Alliance 
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org 
>>>> 
>>>> List Address: [email protected] 
>>>> 
>>>> Change listserver email address & settings: 
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the 
>>>> other: 
>>>> https://www.mail-archive.com/[email protected]/ 
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>>> 
>>>> List rules & etiquette: 
>>>> http://www.re-wrenches.org/etiquette.htm 
>>>> 
>>>> Check out or update participant bios: 
>>>> http://www.members.re-wrenches.org
>>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org
>>> 
>>> List Address: [email protected]
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to