Wrenches, I’m looking to tie in a Generac Powerpact 7.5kW generator with transfer switch to a Sol-Ark 12kW. The Sol-Ark has a two wire start (NO or NC) capability, however, the Generac transfer switch operates on loss of 240V. Is my only option to use a relay driven by the two wire start to drop 240V to the transfer switch?
Thank you, rick brown SolShine Energy Alternatives, LLC Electrical & Solar Contracting Services www.SolShineEnergy.com Check, Virginia 24072 Office: 540.235.3095 Mobile: 540.808.9502 VA Class A Contractor Lic# 2705147660 VA Master Electrician Lic# 2710062762 VA Alternative Energy Systems Installer NABCEP Certified PV Installation Professional 110112-21
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org