Hi Rick,
I have a similar situation with a GE transfer switch, but am curious to
hear what others have to say. My assumption was that the switch transfers
based on loss of 240V from the grid. But I believe (at least with the GE
generator) that the transfer switch sends a two wire start signal to the
inverter when the transfer switch loses the 240V signal. My plan was to
rewire that start signal to the Sol-Ark inverter, but keep the transfer
switch as the main service point to prevent any kind of backfeeding to the
grid.
Cheers,
Dave

On Thu, Jun 17, 2021 at 9:41 AM r...@solshineenergy.com <
r...@solshineenergy.com> wrote:

> Wrenches,
>
> I’m looking to tie in a Generac Powerpact 7.5kW generator with transfer
> switch to a Sol-Ark 12kW. The Sol-Ark has a two wire start (NO or NC)
> capability, however, the Generac transfer switch operates on loss of 240V.
> Is my only option to use a relay driven by the two wire start to drop 240V
> to the transfer switch?
>
> Thank you,
>
> rick brown
> SolShine Energy Alternatives, LLC
> Electrical & Solar Contracting Services
> www.SolShineEnergy.com
> Check, Virginia 24072
> Office: 540.235.3095
> Mobile: 540.808.9502
>
> VA Class A Contractor Lic# 2705147660
> VA Master Electrician Lic# 2710062762
> VA Alternative Energy Systems Installer
> NABCEP Certified PV Installation Professional 110112-21
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 
*Dave Tedeyan, PE*
[image: Sungineer Solar]
1653 Slaterville Road, Ithaca, NY 14850
Cell: 607-288-2898
www.sungineersolar.com
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to