I think you are confusing the transfer switch that can me controlled by the
PWRcell inverter.
All Guardians can be started by two wire control. It does not violate your
warranty. When you start using relays in the transfer switch, that
invalidates your warranty.

On Fri, Jun 18, 2021 at 10:16 AM <[email protected]>
wrote:

> I've controlled Generac Guardians, using the transfer switch and adding
> relays so the inverter decides when it should start. These were out of
> warranty units. Checking with Generac about a proposed new generator, I was
> told that it would void the warranty to do that. I was told that a new
> Generac is supposed to come our around the end of the year that can be
> controlled by an inverter.
>
> Drake
>
>
>
> Drake Chamberlin
>
> Athens Electric LLC
>
> Ohio Electrical Contractor’s License 44810
>
> CO Master Electrician’s License 4526
>
> NABCEP Certified PV Installation Professional
>
> athens-electric.com
>
>
> ---
>
>
>
> On 2021-06-17 09:41, [email protected] wrote:
>
> Wrenches,
>
> I'm looking to tie in a Generac Powerpact 7.5kW generator with transfer
> switch to a Sol-Ark 12kW. The Sol-Ark has a two wire start (NO or NC)
> capability, however, the Generac transfer switch operates on loss of 240V.
> Is my only option to use a relay driven by the two wire start to drop 240V
> to the transfer switch?
>
> Thank you,
>
> rick brown
> SolShine Energy Alternatives, LLC
> Electrical & Solar Contracting Services
> www.SolShineEnergy.com
> Check, Virginia 24072
> Office: 540.235.3095
> Mobile: 540.808.9502
>
> VA Class A Contractor Lic# 2705147660
> VA Master Electrician Lic# 2710062762
> VA Alternative Energy Systems Installer
> NABCEP Certified PV Installation Professional 110112-21
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 
Chris Mason
Solar systems designer
Generac Generators Industrial technician

Comet Systems Ltd DBA Comet Solar
Anguilla Cell  264.235.5670
WhatsApp 264.235.5670
Skype: netconcepts
www.cometsolar.com <http://www.cometenergysystems.com/>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to