Wrenches,

I’m in need of some troubleshooting help on a newly installed system with rapid 
shutdown. System consists 2 SMA SB5.0-1 SP-US-41 (RSD version), RSD devices are 
APS RSD-S-PLC. Each SB is configured with two strings of 9. Modules are REC 
Alpha 360s. 

This system was fully functional for about 1 week before things went awry. 
Initial symptoms were that one of the two strings read 0V 0A on the display 
while the other read ~315V, 5A. The RSD devices output ~700mV each when in the 
off mode (a nice verification feature). I’m reading the correct voltage - 6.75V 
- on both strings when in off mode. Once the Sunny Boy comes on line I’m 
reading around 10V on the faulty string and the correct voltage - ~315V - on 
the other string. 

The above seems to indicate that each RSD is getting sufficient DC voltage from 
the module. Short of pulling each module and doing a visual check what else can 
I look at? How do you isolate a faulty RSD device?

And as luck would have it, everything is functional at the moment. 

Thanks,

rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergy.com
Check, Virginia 24072
O: 540.235.3095
M: 540.808.9502

VA Class A Contractor Lic# 2705147660
VA Master Electrician Lic# 2710062762
VA Alternative Energy Systems Installer  
NABCEP Certified PV Installation Professional 110112-21





_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to