Wrenches, I’m in need of some troubleshooting help on a newly installed system with rapid shutdown. System consists 2 SMA SB5.0-1 SP-US-41 (RSD version), RSD devices are APS RSD-S-PLC. Each SB is configured with two strings of 9. Modules are REC Alpha 360s.
This system was fully functional for about 1 week before things went awry. Initial symptoms were that one of the two strings read 0V 0A on the display while the other read ~315V, 5A. The RSD devices output ~700mV each when in the off mode (a nice verification feature). I’m reading the correct voltage - 6.75V - on both strings when in off mode. Once the Sunny Boy comes on line I’m reading around 10V on the faulty string and the correct voltage - ~315V - on the other string. The above seems to indicate that each RSD is getting sufficient DC voltage from the module. Short of pulling each module and doing a visual check what else can I look at? How do you isolate a faulty RSD device? And as luck would have it, everything is functional at the moment. Thanks, rick brown SolShine Energy Alternatives, LLC Electrical & Solar Contracting Services www.SolShineEnergy.com Check, Virginia 24072 O: 540.235.3095 M: 540.808.9502 VA Class A Contractor Lic# 2705147660 VA Master Electrician Lic# 2710062762 VA Alternative Energy Systems Installer NABCEP Certified PV Installation Professional 110112-21 _______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org