It’s intermittent so I’m hopeful. 

rick brown
SolShine Energy Alternatives, LLC
Electrical & Solar Contracting Services
www.SolShineEnergy.com
Check, Virginia 24072
O: 540.235.3095
M: 540.808.9502

VA Class A Contractor Lic# 2705147660
VA Master Electrician Lic# 2710062762
VA Alternative Energy Systems Installer  
NABCEP Certified PV Installation Professional 110112-21





> On Jun 21, 2021, at 6:29 PM, Carl Adams <[email protected]> wrote:
> 
> 
> APSmart also suggested the thermal camera but that assumes that the 
> array/string is up and running.  If you had a single device that was out and 
> causing the problem that might help pinpoint it but in our case the entire 
> string was offline because the failed RSD was the last module in the string.
> 
> With Kind Regards
> Carl Adams
> SunRock Solar
> 513.290.9072
> 
>> On Mon, Jun 21, 2021, 5:45 PM [email protected] 
>> <[email protected]> wrote:
>> I’m going to try the thermal camera trick before resorting to lifting 
>> modules. 
>> 
>> rick brown
>> SolShine Energy Alternatives, LLC
>> Electrical & Solar Contracting Services
>> www.SolShineEnergy.com
>> Check, Virginia 24072
>> O: 540.235.3095
>> M: 540.808.9502
>> 
>> VA Class A Contractor Lic# 2705147660
>> VA Master Electrician Lic# 2710062762
>> VA Alternative Energy Systems Installer  
>> NABCEP Certified PV Installation Professional 110112-21
>> 
>> 
>> 
>> 
>> 
>>>> On Jun 21, 2021, at 5:42 PM, Jeremy Coxon <[email protected]> 
>>>> wrote:
>>>> 
>>> We are going through a similar scenario right now with APSmart RSD’s and a 
>>> SMA 7.0 that will start up and run, then the next day no start up at dawn.  
>>> Perform a hard reset on inverter and array starts up, runs all day, then 
>>> the next morning we’re back to doing a hard reset to get array to start up. 
>>>  
>>> 
>>> Very simple system 2 strings of 12, voltages at inverter around 8V 
>>> (12x0.7=8.4V) - short run with oversized conductors means very small 
>>> voltage drop thankfully.  SMA says we need to be on site to troubleshoot, 
>>> but without the little APS RSD Eye, I’m thinking they’re just going to say 
>>> it’s not their problem.  APS’s troubleshooting guide basically says lift 
>>> each panel to find the problem.  Not a happy camper!
>>> 
>>> Jeremy Coxon NABCEP 
>>> Certified MWBE
>>> 
>>> Sent from my iPhone
>>> 
>>>>> On Jun 21, 2021, at 12:43 PM, "[email protected]" 
>>>>> <[email protected]> wrote:
>>>>> 
>>>> Carl,
>>>> That’s very helpful. We’ll check each module and report back. 
>>>> 
>>>> rick brown
>>>> SolShine Energy Alternatives, LLC
>>>> Electrical & Solar Contracting Services
>>>> www.SolShineEnergy.com
>>>> Check, Virginia 24072
>>>> O: 540.235.3095
>>>> M: 540.808.9502
>>>> 
>>>> VA Class A Contractor Lic# 2705147660
>>>> VA Master Electrician Lic# 2710062762
>>>> VA Alternative Energy Systems Installer  
>>>> NABCEP Certified PV Installation Professional 110112-21
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>>>> On Jun 21, 2021, at 12:15 PM, Carl Adams <[email protected]> wrote:
>>>>>> 
>>>>> 
>>>>> Rick,
>>>>> I was recently troubleshooting a similar problem.  Open circuit voltage 
>>>>> on all strings was as expected but under load one string was showing 
>>>>> almost no power.  Tracked this down to a failed APSmart device which had 
>>>>> clear signs of thermal damage.  Pictures 1.1 and 1.2.  .
>>>>> A second failed unit some months later had a thermal failure and this one 
>>>>> toasted the module.  Picture 2.1.
>>>>> 
>>>>> These devices can make it difficult to do any meaningful string level 
>>>>> testing.  The devices output a nominal 0.7 volts in open circuit 
>>>>> conditions.  That documentation says this voltage reading is + 25%, so in 
>>>>> theory you could have a number of devices which were not working and your 
>>>>> string voltage would not indicate that.
>>>>> 
>>>>> APSmart does make a test device which can help you verify the 
>>>>> functionality.  The device is called  RSD-EYE+ Detector.  You can contact 
>>>>> YI Kang , APPLICATION & TECHNICAL SUPPORT MANAGER,
>>>>> MLRSD at APSmart for additional information.    737.218.8486
>>>>> <FailedAPSmart1.2.jpg>
>>>>> 
>>>>> <FailedAPSmart2.1.jpg>
>>>>> 
>>>>> <FailedAPSmart1.1.jpg>
>>>>> 
>>>>> With Kind Regards
>>>>> Carl Adams, President
>>>>> SunRock Solar, LLC
>>>>> 513.290.9072 (mobile)
>>>>> 513.766.6025 (office)
>>>>> 
>>>>> 
>>>>> 
>>>>>> On Mon, Jun 21, 2021 at 11:55 AM Lloyd Hoffstatter 
>>>>>> <[email protected]> wrote:
>>>>>> Rick,
>>>>>> I would check with SMA to make sure you have the latest firmware.
>>>>>> 
>>>>>> Best regards,
>>>>>> Lloyd
>>>>>> 
>>>>>> Lloyd Hoffstatter
>>>>>> Sunstruck Consulting
>>>>>> 
>>>>>> Get Outlook for iOS
>>>>>> From: RE-wrenches <[email protected]> on behalf 
>>>>>> of [email protected] <[email protected]>
>>>>>> Sent: Monday, June 21, 2021 11:42:36 AM
>>>>>> To: RE-wrenches <[email protected]>
>>>>>> Subject: [RE-wrenches] RSD Troubleshooting Help
>>>>>>  
>>>>>> Wrenches,
>>>>>> 
>>>>>> I’m in need of some troubleshooting help on a newly installed system 
>>>>>> with rapid shutdown. System consists 2 SMA SB5.0-1 SP-US-41 (RSD 
>>>>>> version), RSD devices are APS RSD-S-PLC. Each SB is configured with two 
>>>>>> strings of 9. Modules are REC Alpha 360s. 
>>>>>> 
>>>>>> This system was fully functional for about 1 week before things went 
>>>>>> awry. Initial symptoms were that one of the two strings read 0V 0A on 
>>>>>> the display while the other read ~315V, 5A. The RSD devices output 
>>>>>> ~700mV each when in the off mode (a nice verification feature). I’m 
>>>>>> reading the correct voltage - 6.75V - on both strings when in off mode. 
>>>>>> Once the Sunny Boy comes on line I’m reading around 10V on the faulty 
>>>>>> string and the correct voltage - ~315V - on the other string. 
>>>>>> 
>>>>>> The above seems to indicate that each RSD is getting sufficient DC 
>>>>>> voltage from the module. Short of pulling each module and doing a visual 
>>>>>> check what else can I look at? How do you isolate a faulty RSD device?
>>>>>> 
>>>>>> And as luck would have it, everything is functional at the moment. 
>>>>>> 
>>>>>> Thanks,
>>>>>> 
>>>>>> rick brown
>>>>>> SolShine Energy Alternatives, LLC
>>>>>> Electrical & Solar Contracting Services
>>>>>> www.SolShineEnergy.com
>>>>>> Check, Virginia 24072
>>>>>> O: 540.235.3095
>>>>>> M: 540.808.9502
>>>>>> 
>>>>>> VA Class A Contractor Lic# 2705147660
>>>>>> VA Master Electrician Lic# 2710062762
>>>>>> VA Alternative Energy Systems Installer  
>>>>>> NABCEP Certified PV Installation Professional 110112-21
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>> 
>>>>>> List Address: [email protected]
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org
>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>> 
>>>>>> List Address: [email protected]
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try 
>>>>>> the other:
>>>>>> https://www.mail-archive.com/[email protected]/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org
>>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>> 
>>>>> List Address: [email protected]
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the 
>>>>> other:
>>>>> https://www.mail-archive.com/[email protected]/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to