On Tue, 20 Jul 2021 10:22:43 -0700, Lorenzo Ortiz 
wrote:  Wrenches,   We have recently had an AHJ reject our Solark 12k
system with Simpliphi batteries stating: _"Energy storage systems are
required to be listed per UL 9540 per NEC 706.5 (See also Annex A in the
NEC, under energy storage systems). THE SOL-ARK SYSTEM IS NOT LISTED AND
TESTED PER UL 9540 BUT IS ONLY LISTED PER UL 1741. THE COMPLETE SYSTEM (IE.
BATTERIES, INVERTER, AND ANY OTHER COMPONENTS ASSOCIATED WITH THE ENERGY
STORAGE SYSTEM) MUST BE LISTED PER UL 9540. Please provide documentation
and certification sheets (from a Nationally Recognized Testing Lab (NRTL))
for both the batteries and SolArk inverter to show that all components are
tested and certified per UL 9540. If it cannot be shown that the batteries
are tested and listed with SolArk inverters per UL 9540, then such system
cannot be installed and a different system that is listed and tested per UL
9540 must be chosen for the project._ _ _ Have any of you run into this
with Solark? Is the plans-checker in the wrong about the entire system
needing to meet the standard and not just the batteries? The code language
is kind of confusing. I can't find any documentation on Solark's website
regarding UL 9540. I know Tesla and Simpliphi have recently put out
documentation regarding this.   Thanks in advance for your help.
   --


Loren Ortiz - Technical Design Specialist 

Board Member  font-family:
Arial; background-color: transparent; vertical-align: baseline;
white-space: pre-wrap;">[email protected] [4] | www.cal-solar.coop [5]


Office: (530) 274-3671   

Fax: (530) 477-7571  CSLB #779624 

Showroom:
149 E Main St. Grass Valley, CA 95945    [6]   

  [7] 

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:[email protected]
[3]
https://californiasolarco.com/
[4] mailto:[email protected]
[5]
http://www.cal-solar.coop/
[6] https://www.nabcep.org/
[7]
https://californiasolarco.com/quote/
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to