Simpliphi has at least two combinations of specific batteries + SolArk that it says are 9540 listed as a combination. See spec sheets/fully integrated systems on their site You may have to dig further to find the actual certificates or whatever the AHJ is asking for. Or maybe these aren’t the combinations you’re looking for.
Brian > On Jul 20, 2021, at 12:05 PM, Dave Angelini Offgrid Solar > <[email protected]> wrote: > > > Sounds like California Loren? > > I use Schneider and they have UL9540 certs. > > Here is a link to them and yes I have been asked this locally. > > https://solar.schneider-electric.com/schneider-electric-solar-and-discover-battery-attain-ul-9540-certification-for-xw-pro-and-aes-batteries/ > > > Dave Angelini Offgrid Solar > "we go where powerlines don't" > http://members.sti.net/offgridsolar/ > e-mail [email protected] > text 209 813 0060 >> On Tue, 20 Jul 2021 10:22:43 -0700, Lorenzo Ortiz <[email protected]> >> wrote: >> >> Wrenches, >> >> We have recently had an AHJ reject our Solark 12k system with Simpliphi >> batteries stating: >> "Energy storage systems are required to be listed per UL 9540 per NEC 706.5 >> (See also Annex A in the NEC, under energy storage systems). The Sol-Ark >> system is not listed and tested per UL 9540 but is only listed per UL 1741. >> The complete system (ie. batteries, inverter, and any other components >> associated with the energy storage system) must be listed per UL 9540. >> Please provide documentation and certification sheets (from a Nationally >> Recognized Testing Lab (NRTL)) for both the batteries and SolArk inverter to >> show that all components are tested and certified per UL 9540. If it cannot >> be shown that the batteries are tested and listed with SolArk inverters per >> UL 9540, then such system cannot be installed and a different system that is >> listed and tested per UL 9540 must be chosen for the project. >> >> Have any of you run into this with Solark? Is the plans-checker in the wrong >> about the entire system needing to meet the standard and not just the >> batteries? The code language is kind of confusing. I can't find any >> documentation on Solark's website regarding UL 9540. I know Tesla and >> Simpliphi have recently put out documentation regarding this. >> >> Thanks in advance for your help. >> >> -- >> >> >> Loren Ortiz - Technical Design Specialist >> Board Member & Worker Owner >> [email protected] | www.cal-solar.coop >> Office: (530) 274-3671 >> Fax: (530) 477-7571 CSLB #779624 >> Showroom: 149 E Main St. Grass Valley, CA 95945 >> >> >> >> >> >> >> >> > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org

