Okay Is there a quick way to run on just one string? Or should I say determine which batteries would make a good string. I’d normally say, find the best batteries based on specific gravity and use them, but in this case all specific gravity‘s seem good.
Jeremy Rodriguez Solar Installation / Design Expert All Solar, Inc. 1453 M St Penrose Colorado 81240 Sent by Jeremy's iPhone. Sorry for typos and shorthand. On Jul 21, 2021, at 8:44 AM, Steve Higgins <[email protected]> wrote: FLA batteries cells fail generally in two manners. Open Cell and Shorted. Open Cells are more resistive and "Eat up" charging voltage which denies voltage and charging potential to the rest of the bank so the entire bank sags. This is the most common type of failure. Shorted Cells are less resistive so they allow voltage and current to pass on to the rest of the cells in the string. This causes an overcharge condition because the dead cell isn't dropping any voltage and the rest of the cells in the string become "overcharged". Sometimes SG's will look good, but when the bank is under load you will see the voltage drop off quickly. This is often the shorted cell. Battery SG's are like Goldilocks and the three bears.. There is too high... Too low and Just right... Too low and you lose capacity and this causes sulfation, which will cause overheating, excessive water use, and will lead to failure. This is the most common way an FLA battery bank dies is low SG's are not corrected soon enough and the bank sulfates. Too high, and you'll get great capacity, for a while, but that higher acidity will cause corrosion on the plates which will act a lot like sulfation. On these, you will often see a darker electrolyte as the higher acidity/corrosion is eating away at the active material of the plates. To figure this out what you need to do is... 1. Charge the bank to what you think is full or close to it.. 2. Find the 10 Hour Discharge Rate of the bank. (C/10 Discharge Current) 3 Apply load as close as you can get it by running loads in the house. You will be running this test for 2-5 hours depending on test results. 4. Monitor battery voltages during this test every 30-60 mins. individual battery voltages should stay pretty close to each other as they discharge, If you start to see one or two batteries sag in voltage before the rest you have weak or dying cells. My bet is you have 1 or two cells that have failed and this is the reason for the LBCO... <http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com><http://www.rollsbattery.com>[https://imgur.com/hENEoQQ.png]<http://www.rollsbattery.com> Steve Higgins ⋅ Technical Services Manager t +1.902.597.4020 m +1.206.790.5840 f +1.902.597.8447 e [email protected]<mailto:[email protected]> <http://www.facebook.com/RollsBattery>[http://cdn3.iconfinder.com/data/icons/free-social-icons/67/facebook_square_gray-24.png]<http://www.facebook.com/RollsBattery> [http://cdn3.iconfinder.com/data/icons/free-social-icons/67/twitter_square_gray-24.png] <http://www.twitter.com/RollsBattery> [http://cdn3.iconfinder.com/data/icons/free-social-icons/67/youtube_square_gray-24.png] <https://www.youtube.com/user/RollsBattery> [http://cdn3.iconfinder.com/data/icons/free-social-icons/67/linkedin_square_gray-24.png] <https://www.linkedin.com/company/rolls-battery-engineering> <http://www.instagram.com/RollsBattery> <http://www.instagram.com/RollsBattery> [https://cdn3.iconfinder.com/data/icons/free-social-icons/67/instagram_square-24.png] <http://www.instagram.com/RollsBattery> ________________________________ CONFIDENTIALITY: The information transmitted herein is intended only for the addressee and may contain confidential, proprietary and/or privileged material. Any unauthorized review, distribution or other use of or the taking of any action in reliance upon this information is prohibited. If you receive this email in error, please contact the sender and delete or destroy this message and all copies. ________________________________ On Wed, Jul 21, 2021 at 7:24 AM Jay <[email protected]<mailto:[email protected]>> wrote: And what color is the electrolyte? On Jul 21, 2021, at 8:02 AM, Jay <[email protected]<mailto:[email protected]>> wrote: Hi Jeremy I would like to know brand and model of battery first. Jay Peltz power On Jul 21, 2021, at 7:22 AM, Jeremy Rodriguez <[email protected]<mailto:[email protected]>> wrote: What’s going on with a battery bank that reads 1.275 SG on all the batteries but one, which has cell readings slightly higher. The bank is probably 7 years old and this is not a full time residence. It’s shutting down with LBCO error. I need to go check the site, but I’d expect a dead or weak cell here. What else can be checked , battery wise? Jeremy Rodriguez Solar Installation / Design Expert All Solar, Inc. 1453 M St Penrose Colorado 81240 Sent by Jeremy's iPhone. Sorry for typos and shorthand. _______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected]<mailto:[email protected]> Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org _______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected]<mailto:[email protected]> Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org _______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.membe
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org

