Adam, I assume it’s a NYSERDA inspector that’s pushing back, correct? We’ve dealt with this issue a number of times, and while I will argue until I’m blue in the face that the code does not consider the inside of a properly installed NEMA 3R enclosure a damp/wet location, NYSERDA has not accepted that argument.
To be clear, the Buchanan splice caps and insulators are only rated for dry locations. I’ve heard that NYSERDA has allowed them to be used with dielectric gel applied to the interior of a splice cap insulator, but have not been able to confirm. Best Regards, Isaac Opalinsky | Director, Applications & Technical Support mobile 443-277-6286 | [email protected]<mailto:[email protected]> [sp_2014_logo_black_orange_CMYK-01] From: RE-wrenches <[email protected]> On Behalf Of AE Solar Sent: Monday, August 16, 2021 2:55 PM To: RE-wrenches <[email protected]> Subject: [EXT] [RE-wrenches] Buchanan Crimps in Outdoor Boxes External Email - Use caution when responding, clicking, and/or downloading attachments. ________________________________ Wrenchers, Some point back we transitioned from polaris lugs to buchanan crimps/caps (doping our wires in noalox) for our jbox splices. I know there have been a few conversations on here about this. Seems like a much more robust connection than anything we have used prior. But now we have an inspector who isn't in support of using them for outdoor/damp locations. To be fair (although it seems like a far superior connection) Ideal doesn't have documentation to support outdoor use. I know a lot of folks on here have had solid/long lasting results though. In any event, we may have to transition away from buchanan crimps and wondering what you all recommend as your second (or first) choice? Or if anyone has experience with supporting this application when dealing with inspectors? Do we go back to polaris lugs? I know there was a conversation a while back about failures with those... Thanks for any thoughts. Adam Adam Katzman Autonomous Energies PO Box 1245 Kingston, NY 12402 www.autonomousenergies.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.autonomousenergies.com&d=DwMFaQ&c=Kv2S0ZicsIm17HTFqYG_Og&r=RD0lHHgQqAl7xvyDm5AiPkLCedjBloPiZPB0MsAPMCE&m=_mjHpHDfeE0DA7KJAxQp-6Q_uNnHsFLwm52PqJ_Zugw&s=TvRw39ewcR48vbSFcdNGGl_zKXV7wLvhwtjdxDX2v_w&e=> (518) 567-1468
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org