William,

Yes, I think we both agree - the SolarEdge system should be designed *and
listed* to work with 600 VDC modules, even if the optimizer-output side is
running at 850 VDC. Has SolarEdge given you any indication about whether
this is a supported setup?

August





On Thu, Sep 9, 2021 at 10:11 AM William Miller <will...@millersolar.com>
wrote:

> August:
>
>
>
> I am not worried about the inverter backfeeding.  I only brought that up
> because there was a precedent set that in order to rule out an electronic
> assembly backfeeding, it had to be listed as such.
>
>
>
> Here is what I am worried about:  I am worried about the high voltage on
> the output of an optimizer crossing over the optimizer in a failure
> condition and energizing the input circuit of the optimizer.
>
>
>
> If I understand the design process correctly, manufacturing to high
> standards is not enough—a listing with a recognized agency to that effect
> is also required.
>
>
>
> Thanks again for thinking and writing about this.  Your experience and
> expertise is valued.
>
>
>
> William
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* August Goers [mailto:aug...@luminalt.com]
> *Sent:* Thursday, September 9, 2021 9:34 AM
> *To:* William Miller
> *Cc:* RE-wrenches; Greg Notley; jonathan.sm...@solaredge.com;
> rya...@solaredge.com; Garrett Duffy
> *Subject:* Re: [RE-wrenches] "Re-powering" Aging Utilty Scale PV systems
>
>
>
> Hi William - I think I'm picking up on a couple of separate issues here.
> First, the question is whether you can install a module rated for 600 VDC
> max on a 1000 VDC SolarEdge system. I realize that the article I linked to
> was talking about string combiners and currents, but the isolation between
> the module side and output side of the optimizer was the point. The max
> input voltage on the optimizers is less than 100 VDC, so it would seem safe
> to connect a module rated at 600 VDC. Keep in mind that this is just the
> maximum system voltage, not the Voc, Vmp, etc. Still, I would want to
> verify this with SolarEdge prior to proceeding with system design.
>
>
>
> Your second issue related to whether the inverter will backfeed in a fault
> condition is addressed in that article. I haven't done my homework to know
> whether the inverter listings test for this particular fault situation. I
> know that most string inverters (or maybe all?) that we've designed with
> over the last 15 years say that they don't contribute reverse fault
> current, so we don't count that current in our calculations for fusing. So
> getting back to your question - what happens if the optimizers fail, will
> modules be destroyed too? I'm sure SolarEdge's design team hopes the answer
> is no. Depending on how they fail, who knows? Let's hope they are designed
> and manufactured to the highest standards.
>
>
>
> August
>
>
>
>
>
>
>
> On Wed, Sep 8, 2021 at 11:11 PM William Miller <will...@millersolar.com>
> wrote:
>
> August:
>
>
>
> I realized I made a poor choice of words in one place below.  When I wrote
> “fused components” I met melted together in a heat failure, not protected
> by an overcurrent fuse.
>
>
>
> Wm
>
>
>
>
>
> August:
>
>
>
> Thank you for the thoughtful reply.  I have come to know I can count on
> you for that.
>
>
>
> The article you site is interesting, but I do not think it applies.  The
> article is about current in strings, not voltages.
>
>
>
> This interpretation of considering string currents was first introduced to
> me by John Berdner (remember him?) in this article
> <https://millersolar.com/MillerSolar/Resources/ul_fuses.pdf>.  The John
> Berdner white paper is essentially the same information as in the Solar
> Edge article you cited and is essential information.
>
>
>
> What is most interesting to me in John’s article is 690.9(A) FPN.  It
> points out that one cannot ignore the possibility of backfeed from
> inverters.
>
>
>
> I have on occasion, when using this 690.9(A) exception to avoid combiner
> fuses, been required by plan checkers to provide documentation from an
> inverter manufacturer that the inverter proposed was UL certified to not be
> capable of providing backfeed current.  This is in spite of any intuition
> that one might solidly hold that inverters can’t backfeed DC current.  It’s
> not true just because it seems impossible, or even if the manufacturer says
> so, it’s only true if a listing agency says it is true.
>
>
>
> The question I am asking applies to voltage isolation:  If I have 850
> volts on the output of an optimizer and the optimizer fries, is there any
> possibility that fused components could connect the 850 volts to the input
> of the combiner?  Most importantly, does a listing agency say it is not
> possible?  If it is not certified, then using optimizers is not a design
> option.
>
>
>
> Three persons from Solar Edge have told me the isolation is infallible.
> I’m not trying to be difficult, but I really think this assertion has to
> confirmed by a listing agency.  I have not seen that yet.
>
>
>
> Solar Edge has been quick to reply to my voicemails and has expressed a
> real interest in this project, much to their credit.  I will press this
> point to them and I will post to this forum what I learn.
>
>
>
> By the way, I am sure you have not forgotten a recent flurry of posts on
> this site recently about rapid shut down device(s) frying in use.
> Optimizers are similar devices in the same demanding environment and
> exposed to high voltages as well.  Equipment failure is always a
> possibility.
>
>
>
> Thanks again to those many participants who have replied to my question.
> I am much smarter because of my wrench forum friends.
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> *From:* August Goers [mailto:aug...@luminalt.com]
> *Sent:* Wednesday, September 8, 2021 4:44 PM
> *To:* William Miller; RE-wrenches
> *Subject:* Re: [RE-wrenches] "Re-powering" Aging Utilty Scale PV systems
>
>
>
> Hi William - You raise a great question - can you install 600 VDC modules
> on a 1000 VDC SolarEdge system? Of course the DC optimizer output circuit
> would need to be rewired with 1000 VDC wiring and connectors, but I think
> the answer is "yes." According to this article
> <https://www.solaredge.com/sites/default/files/application_notes_string_combiners_na.pdf>,
> "In a SolarEdge system, the PV modules are isolated from the DC output
> circuit by the power optimizer." To me, it sounds like there is no risk of
> going over the max optimizer input voltage. I would want to verify this
> with SolarEdge prior to designing any systems, but it seems like a good
> idea to explore!
>
>
>
> I was recently on another group chat, and someone mentioned being in a
> similar predicament to you. They want to upgrade an old central inverter.
> Anyway, they had found that the SMA CORE1 33 kW unit at least can be strung
> up to work with 600 VDC modules and wiring:
> https://files.sma.de/downloads/STPCORE1-DS-en-28.pdf?_ga=2.30799225.717469396.1631144387-1894865662.1631144383
>
> I'm sure you'd have to redo a lot of the conduit and wire to accommodate
> several smaller inverters, but this might be worth exploring as well.
>
>
>
> August
>
> Luminalt
>
>
>
>
>
> On Wed, Sep 8, 2021 at 4:13 PM William Miller <will...@millersolar.com>
> wrote:
>
> Friends:
>
>
>
> I learned a new buzzword recently:  “Re-powering.”  It means replacing
> inverters on an existing PV system of ten or more years old.  Due to the
> high number of systems of this vintage it appears that re-powering has
> become somewhat of a sub-industry.  The big problem is these systems are
> all 600 Volt  limited PV panels, combiners and re-combiners and there are
> no 600 volt utility grade inverters being manufactured.
>
>
>
> I am working on a utility scale system
> <https://millersolar.com/MillerSolar/Portfolio/Commercial/CommercialTracker/CommercialTracker.html>
> built about 14 years ago that fits the description above.  There are two
> 250KVA Xantrex GT250 inverters and one has failed.  The question of the
> moment is:  Repair or replace?
>
>
>
> Repair:  If we fix these inverters, can we count on support in the
> future?    We can negotiate a service contract with Schneider at a cost yet
> to be revealed.  This requires we buy a spare parts kit for about $100K.
> There are a few other companies that claim to offer repair services on
> these inverters but none has followed through.
>
>
>
> Replace:  The PV plant is built with panels and BOS all limited to 600 VDC
> max.  There are no more 600 volt input utility scale inverters being built,
> or at least none that I have found.  If we install a 1000 or 1500 volt
> inverter we may have to replace the entire PV array and BOS.  It may be
> possible to convert the output of the existing panels to a higher voltage
> with DC-DC converters.
>
>
>
> Here are the options I see:
>
>
>
> Optimizers: One purveyor of optimizers is Solar Edge.  Solar Edge offers a
> 100 KVA inverter.  This inverter requires DC input of 850 volts.  The
> inverter requires optimizers to obtain this voltage.  The question:  Do the
> optimizers isolate the PV from the higher string voltages in the case of a
> catastrophic failure of one or more of the optimizers?
>
>
>
> Repower with outboard DC-DC voltage converters, such as provided by
> Alencon Systems.  Solectria has successfully done this.  Here
> <https://alenconsystems.com/learning/pv-retrofits-with-transformerless-inverters/>
> is a paper on the subject.
>
>
>
> If anyone has dealt with this issue before I would sure appreciate any
> wisdom.
>
>
>
> Here is a link
> <https://millersolar.com/MillerSolar/case_studies/30-Re-Powering/re-powering.html>
> to a web-page I built for this project.
>
>
>
> Thanks,
>
>
>
> William Miller
>
>
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com
>
> CA Lic. 773985
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to