It's been a long time, but I'm quite certain it was landed on the Gen (AC2)
input bus. It worked fine for many months, so I can't imagine this is the
issue, but it's worth double checking.

This was a prewired dual Radian system from Wholesale Solar (or whatever
they're called now).

Jason


On Tue, Nov 2, 2021, 6:41 PM Maverick Brown <[email protected]>
wrote:

> Sounds like the generator is connected to AC Out terminals (AC coupling).
> This will ‘work’ to charge batteries. It will function but the Radian has
> no way to regulate battery voltage. One would typically install an AUX
> controlled AC relay on a grid tie inverter set up for AC coupling. In your
> case, make sure the generator is landed on the generator terminals, AC2.
>
> Maverick Brown
> Off-Grid Solar Commander since 2006
> *Maverick Solar Enterprises, Inc.*
> * • Solar Commander Remote Power*
>
> * • SunFlow Systems Cathodic Protection *[email protected]
> 512-460-9825
>
>
> On Nov 2, 2021, at 3:46 PM, Jason Szumlanski <
> [email protected]> wrote:
>
> 
> Whoa! I just got access to his OpticsRE. It says battery voltage reached
> as high as 66V!!! (48V Nominal). I don't know if that's true yet or a
> acrtually voltage metering issue. But it appears that when the generator
> stops the invert mode kicks in and immediately shuts down due to high
> battery voltage. I guess the inverters were coming back alive when the
> voltage settled to the normal range. But the homeowner reports that when he
> manually restarts the system the battery is around 54V. I'm not sure how
> long after the shutdown this occurs.
>
> So at this point I told him he needs to be very careful and make sure he's
> not cooking the batteries by testing with a volt meter during charging to
> see what's really going on.
>
> I'm concerned because the FNDC, both GS8048s and both FM100s all report
> abnormally high battery voltage. That suggest that the voltage is actually
> that high. But the charger setpoints are clearly set to defaults for absorb
> and float. I don't know why the voltage would blow past the setpoints.
>
> I misspoke in my initial email. He has AGS voltage start and SOC start set
> up.
>
>
>
>
> On Tue, Nov 2, 2021 at 3:09 PM Jason Szumlanski <
> [email protected]> wrote:
>
>> I have a client (DIY) who has dual 8048's and he is starting the
>> generator using both high load and low voltage settings with the AGS. It
>> worked flawlessly for 9 months. Then for a couple of months when the
>> generator shut down the lights would flicker. Eventually it started
>> shutting down his loads completely for a couple of minutes and it would
>> start back up automatically. Now when the generator shuts down the
>> inverters shut down and need to be restarted manually.
>>
>> He said there is an error code but he never wrote it down.
>>
>> Any ideas given the sequence of events?
>>
>> Lead acid batteries. 20kW generator. Despite it being DIY from an online
>> wholesaler, he did hire a licensed electrician and that electrician
>> consulted with me a bit prior to installation, so it's a pretty good job.
>> I'm thinking it's an internal Radian setting or fault causing this.
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to