You can find the temperature compensation voltage in the battery hot button. 
It might be a bad temp sensor

jay

peltz power

> On Nov 2, 2021, at 2:46 PM, Jason Szumlanski 
> <[email protected]> wrote:
> 
> Whoa! I just got access to his OpticsRE. It says battery voltage reached as 
> high as 66V!!! (48V Nominal). I don't know if that's true yet or a acrtually 
> voltage metering issue. But it appears that when the generator stops the 
> invert mode kicks in and immediately shuts down due to high battery voltage. 
> I guess the inverters were coming back alive when the voltage settled to the 
> normal range. But the homeowner reports that when he manually restarts the 
> system the battery is around 54V. I'm not sure how long after the shutdown 
> this occurs.
> 
> So at this point I told him he needs to be very careful and make sure he's 
> not cooking the batteries by testing with a volt meter during charging to see 
> what's really going on.
> 
> I'm concerned because the FNDC, both GS8048s and both FM100s all report 
> abnormally high battery voltage. That suggest that the voltage is actually 
> that high. But the charger setpoints are clearly set to defaults for absorb 
> and float. I don't know why the voltage would blow past the setpoints. 
> 
> I misspoke in my initial email. He has AGS voltage start and SOC start set 
> up. 
> 
> 
> 
> 
> On Tue, Nov 2, 2021 at 3:09 PM Jason Szumlanski 
> <[email protected] 
> <mailto:[email protected]>> wrote:
> I have a client (DIY) who has dual 8048's and he is starting the generator 
> using both high load and low voltage settings with the AGS. It worked 
> flawlessly for 9 months. Then for a couple of months when the generator shut 
> down the lights would flicker. Eventually it started shutting down his loads 
> completely for a couple of minutes and it would start back up automatically. 
> Now when the generator shuts down the inverters shut down and need to be 
> restarted manually. 
> 
> He said there is an error code but he never wrote it down.
> 
> Any ideas given the sequence of events?
> 
> Lead acid batteries. 20kW generator. Despite it being DIY from an online 
> wholesaler, he did hire a licensed electrician and that electrician consulted 
> with me a bit prior to installation, so it's a pretty good job. I'm thinking 
> it's an internal Radian setting or fault causing this. 
> 
> Jason Szumlanski
> Florida Solar Design Group
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to