It was tough for me to figure out how to write my email and not make it confusing.

What I am worried about is the microinverter system operating when the utility goes down and the microinverters continuing to operate and charge the batteries as a load.  I need to disconnect the microinverter circuit only when the batteries are fully charged in grid isolated mode.  All the ways I can think of that would normally work to deenergize the microinverters automatically based upon battery voltage won't work.  I can submit a drawing if that would help. I am trying not to run another conductor circuit from the house to the garage.  I realize that would solve the problem, but it is an expensive solution.  English is my foreign native language.


On 11/23/2021 10:39 AM, August Goers wrote:
Hi Chris - If I'm following you right, you have a PV system on a detached garage that ties into a backup subpanel also in the garage? The code only requires the RSID (rapid shutdown initiation device) to be on the exterior of the building. Would it work to put the RSID on the garage exterior? You could route your PV circuits to a switch or switches on the exterior of the garage on the way down to the sub it ties into. You could also use a shunt trip breaker(s) for the PV circuit(s). If for some reason you need to have the RSID on the main house, it gets trickier. Might need to trench?

August
Luminalt


On Tue, Nov 23, 2021 at 7:24 AM Christopher Warfel <[email protected]> wrote:

    I would appreciate ideas on how to shut down a proposed
    microinverter system on a garage that is 100% serviced by an
    Outback Radian multimode system in the main building that has the
    garage on the back up service panel in the main building.

    Garage has a MLO subpanel that is connected to the multimode back
    up service panel that is in the main building.

    If grid goes down, we need to disconnect the microinverter array
    so it does not overcharge the battery system. If we use the
    battery voltage relay, we will take out all the garage circuits,
    which would disable its heating system, etc. We just want to
    disconnect the microinverter circuit in the garage subpanel.

    Does anyone know of a product that could do this. I would imagine
    a transmitter, or perhaps something else besides a microinverter
    array?


    Thanks for any help. Chris




--                         Christopher Warfel
    ENTECH Engineering, Inc.
    PO Box 871, Block Island, RI 02807
    401-466-8978
    <http://entech-engineering.com>


    _______________________________________________
    List sponsored by Redwood Alliance

    Pay optional member dues here: http://re-wrenches.org

    List Address: [email protected]

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    There are two list archives for searching. When one doesn't work,
    try the other:
    https://www.mail-archive.com/[email protected]/
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    http://www.re-wrenches.org/etiquette.htm

    Check out or update participant bios:
    http://www.members.re-wrenches.org

--
            Christopher Warfel
                     ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                401-466-8978
<http://entech-engineering.com>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to