You can use the frequency shift in the radian inverter to shut down the micros. Yes gets to 64hz but probably not going to happen very often?
Or you could find a remote controlled relay controlled via the radian aux relay. Jay Peltz power. > On Nov 23, 2021, at 7:39 AM, August Goers <[email protected]> wrote: > > > Hi Chris - If I'm following you right, you have a PV system on a detached > garage that ties into a backup subpanel also in the garage? The code only > requires the RSID (rapid shutdown initiation device) to be on the exterior of > the building. Would it work to put the RSID on the garage exterior? You could > route your PV circuits to a switch or switches on the exterior of the garage > on the way down to the sub it ties into. You could also use a shunt trip > breaker(s) for the PV circuit(s). If for some reason you need to have the > RSID on the main house, it gets trickier. Might need to trench? > > August > Luminalt > > >> On Tue, Nov 23, 2021 at 7:24 AM Christopher Warfel >> <[email protected]> wrote: >> I would appreciate ideas on how to shut down a proposed microinverter system >> on a garage that is 100% serviced by an Outback Radian multimode system in >> the main building that has the garage on the back up service panel in the >> main building. >> >> Garage has a MLO subpanel that is connected to the multimode back up service >> panel that is in the main building. >> >> If grid goes down, we need to disconnect the microinverter array so it does >> not overcharge the battery system. If we use the battery voltage relay, we >> will take out all the garage circuits, which would disable its heating >> system, etc. We just want to disconnect the microinverter circuit in the >> garage subpanel. >> >> Does anyone know of a product that could do this. I would imagine a >> transmitter, or perhaps something else besides a microinverter array? >> >> >> >> Thanks for any help. Chris >> >> >> >> >> >> >> >> -- >> Christopher Warfel >> ENTECH Engineering, Inc. >> PO Box 871, Block Island, RI 02807 >> 401-466-8978 >> <EEIlogolong.jpg> >> >> >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> >> List Address: [email protected] >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/[email protected]/ >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org >> > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org

