Lones,
Thanks for the attempted direct communication via phone - sorry I didn't
catch it.
I appreciate the clarification about the system logic and what the issue
seems to have been.  I am still confused as to why the system would leave
the generator running after it decided it was done charging based on the
settings. I understand that the SOC start/stop charging was much tighter
than would typically be desirable, but I don't understand why that would
create the generator "run on" after those parameters were met.
I ask in part because my experience with the original Mate on VFX systems
is what appears to be a software glitch or a minor component failure, where
the AGS system fails to send a signal to the generator to start based on
programmed parameters.  It is odd since it seems to work sometimes and then
not at other times.  The issue seems to appear after the mate is several
years old, and the only way I've been able to fix the problem is to replace
the mate, and then the system works fine. (Sorry to sort of hijack this
thread).
Howie

*Howie Michaelson**Sun Catcher*

*NABCEP Certified Solar PV Installer™*

*Solar Electric Systems Sales & Service802-272-0004*


On Fri, Jan 14, 2022 at 3:42 PM Tuss, Lones <[email protected]> wrote:

> Hello Howie
>
> I  believe the situation was this.
>
> The gen would automatically start ..as it should.
>
> The inverter would accept the ac source… as it should.
>
> It would begin a charge sequence again …as it should.
>
> But
>
> The inverter would shut off the generator within a very short amount of
> time.
>
> Usually this is caused by a start condition initiating a gen run.
>
> But some other stop condition causing the gen to be turned off.
>
> With 3 different run stop conditions used in the Mate3S it was just a
> matter of making thing a little more simple. I disabled the SOC run/stop in
> the Mate3S AGS just to see if that was the cause of the stop command.
>
> Doing a 2 minute  voltage start will cause the  gen to run until the
> absorb timer on the inverter has zeroed out. Indeed it did. The Soc command
> was set to start at 80 or 82% (I forget which) and Stop at 90% as requested
> by the customer.
>
> Both Mac and I agreed this was a bit crazy but it was what the customer
> wanted.
>
> By looking in the Optics Event logs the shut down was attributed to the
> Stop SOC condition being met.
>
> So eliminating SOC was a logical first step.
>
>     To me the only remaining question is I did not see the SOC reach 90%
> but that is a pretty tight window in which to operate. A more usual SOC
> start /stop  condition would be 60%to 90% with a 100% charge required every
> so often (user selectable). I believe this system was set for 100% charge
> every 14 Days.
>
> I hope this helps explain without adding further confusion.
>
> Take Care All
>
>
>
> *From:* RE-wrenches <[email protected]> *On
> Behalf Of *Howie Michaelson
> *Sent:* Thursday, January 13, 2022 2:42 PM
> *To:* RE-wrenches <[email protected]>
> *Subject:* Re: [RE-wrenches] Radian Glitch
>
>
>
> *CAUTION:* This email originated from outside of the Company. Do not
> click links or open attachments unless you recognize the sender and know
> the content is safe.
>
>
>
> Thanks for the update Lines. While it seems from turning off the soc gen
> control, the generator is running as it should, I don't understand how that
> explains the charging behavior, or why the inverter continued to ruin the
> generator without using it's output.
>
> Howie
>
> Howie Michaelson
> Sun Catcher
> NABCEP Certified Solar PV Installer™
> Solar Electric & Heat Pumps Systems Sales & Service
> 802-272-0004
>
>
>
> On Thu, Jan 13, 2022, 1:32 PM Tuss, Lones <[email protected]> wrote:
>
> Hello Wrenches
>
> I was able to contact Mac this morning. Luckily this system was on optics
> so we were able to go look at the start and stop conditions in the AGS
> programming and the Event logs.
>
> The event logs stated the stop was caused by an SOC stop command.
>
> In AGS this system is using 3 start conditions
>
> Voltage start , Load start and  Soc start
>
> At the customer’s request the Soc is set to start at 82 % and stop at 90%
>
> Which seems a little crazy to both Mac and I
>
> But to test if the Soc was indeed the cause of the short run.
>
> We disabled the SOC start/stop.
>
> We then started a bulk cycle to set the absorb timer to the 2 hr time
> limit as programmed in the inverter.
>
> We raised the 2 minute timer above the current battery voltage to initiate
> a gen run.
>
> The gen did start and at this point the gen has run for approximately 1.5
> to 2 hours.
>
> So it does appear that  SOC stop was the cause of the short run, as
> indicated in the event Log.
>
> What neither or Mac or myself can explain is the graph on the Dashboard
> does not show the Soc above
>
> 80%  I am not certain if it is due to a momentary spike that is too quick
> to record. At this point that is just a guess (sorry). But that is the
> situation.
>
>    I will say it was nice to have this on Optics as we could go visit the
> site and do everything from our respective homes.
>
> Mac thank you for returning my call and working through this issue.
>
> Take Care All
>
>
>
>
>
>
>
>
>
>
>
>
>
> *From:* RE-wrenches <[email protected]> *On
> Behalf Of *Mac Lewis
> *Sent:* Thursday, January 13, 2022 4:38 AM
> *To:* RE-wrenches <[email protected]>
> *Subject:* [RE-wrenches] Radian Glitch
>
>
>
> *CAUTION:* This email originated from outside of the Company. Do not
> click links or open attachments unless you recognize the sender and know
> the content is safe.
>
>
>
> Good Morning Wrenches,
>
>
>
> I have an Outback Radian 8048 site that is acting up.
>
>
>
> This only happens when the generator is automatically started.
>
> It will start the generator and warm it up normally and then connect and
> start charging as it should.  After about 30 seconds to 1 minute it will
> drop the AC input, and put the generator in cool down mode and the charger
> will be disabled.  It will then continue to run the generator until you
> turn it off manually, presumably because it hasn't reached the stop
> trigger.
>
>
>
> This system will charge normally when the generator is manually started.
> The firmware on the Mate3s is up to date.
>
>
>
> Any ideas?
>
>
>
> Thanks in advance
>
>
>
> --
>
>
>
>
>
>
>
> Mac Lewis
>
> "Yo solo sé que no sé nada." *-Sócrates*
>
>
>
> This email and any attachments may contain confidential information that
> is intended only for the recipient(s). If you have received this email in
> error, please notify the sender and delete it from your system. Any views
> or opinions presented in this email are solely those of the author and do
> not necessarily represent those of the company or its affiliates. This
> email does not constitute an agreement to conduct transactions by
> electronic means and does not create any legally binding contract or
> enforceable obligation in the absence of a fully signed written contract.
> The recipient should check this email and any attachments for viruses. The
> company accepts no liability for any loss or damage caused by software
> viruses. If you are the intended recipient and you do not wish to receive
> similar email(s) from us in the future then please notify the sender.
> Please consider the environment before printing.
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
> <https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-7b396d10a42c0f44&q=1&e=aa159a9a-8607-4e25-b583-41a420f8a086&u=http%3A%2F%2Fre-wrenches.org%2F>
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-a1bff427848a4564&q=1&e=aa159a9a-8607-4e25-b583-41a420f8a086&u=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> <https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-e399d9bb5547f820&q=1&e=aa159a9a-8607-4e25-b583-41a420f8a086&u=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2F>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-b8ea30cbc06c75b2&q=1&e=aa159a9a-8607-4e25-b583-41a420f8a086&u=http%3A%2F%2Flists.re-wrenches.org%2Fpipermail%2Fre-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-c65f2c4f8389e144&q=1&e=aa159a9a-8607-4e25-b583-41a420f8a086&u=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> <https://protect2.fireeye.com/v1/url?k=31323334-501d2dca-31313abf-454455534531-3373bc454b22cb3c&q=1&e=aa159a9a-8607-4e25-b583-41a420f8a086&u=http%3A%2F%2Fwww.members.re-wrenches.org%2F>
>
>
>
> This email and any attachments may contain confidential information that
> is intended only for the recipient(s). If you have received this email in
> error, please notify the sender and delete it from your system. Any views
> or opinions presented in this email are solely those of the author and do
> not necessarily represent those of the company or its affiliates. This
> email does not constitute an agreement to conduct transactions by
> electronic means and does not create any legally binding contract or
> enforceable obligation in the absence of a fully signed written contract.
> The recipient should check this email and any attachments for viruses. The
> company accepts no liability for any loss or damage caused by software
> viruses. If you are the intended recipient and you do not wish to receive
> similar email(s) from us in the future then please notify the sender.
> Please consider the environment before printing.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other: