Install the newest firmware for the Gateway(Your gonna need one) and the Pro. 
Then get into region settings and try one until it works. I can’t recall which 
one. We’ve had to do this to the dozen or so XW Pros we’ve installed to get 
them to play nice with generators. Once they are set up, they work without 
glitches.

> On Feb 11, 2022, at 8:49 AM, Kevin Pegg <[email protected]> wrote:
> 
> Hello Wrenches, 
>  
> I am setting up my first XW Pro in an off-grid dual generator config. I did 
> not intend on the Pro version but it was all I could obtain for this job. On 
> AC1 With the factory default settings of 55/65 Hz min max, and the gen 
> running at 62 Hz unloaded it just refused to qualify the power even though it 
> was within spec. By lowering RPM to 61.5 Hz it then will qualify fine. 
> Curious. AC2 does not have this issue even small portable gens will synch and 
> charge fine.
>  
> The challenge I am having now is sometimes it will qualify the generator 
> power, engage and charge, but sometimes it will just engage AC Passthrough 
> and refuse to charge, either manual gen run or automatic by low battery 
> condition. Obviously a problem when gen auto starts but then refuses to 
> charge.  
>  
> Is there a way to program this inverter to be more off-grid friendly? I am 
> assuming AC1 which is normally for grid input has a lot tighter tolerances, 
> even if programming suggests otherwise.
>  
> Thanks, 
> Kevin
>  
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/ 
> <https://www.mail-archive.com/[email protected]/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>



        Michael Morningstar

        Morningstar Electric
        PO Box 1494
        Mount Shasta, California 96067
        530-921-0560
        CSLB 949635
 
  

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to