I have about 1200 ft from float switches, two in parallel, to the CU200 and 
another 200 ft to the pump without any issues. If there is bad connection it 
could be a problem though. 

Brad

Sent from my iPhone

> On Feb 25, 2022, at 12:17 PM, Nick Soleil <[email protected]> wrote:
> 
> Hi Jay,
> 
> Is it a long wire length?  I had a similar issue with a Aquavar Solo2 pump 
> controller recently where the float switch was not turning the pump off.  The 
> wire length from the float switch to the pump controller was over 300ft and 
> ran underneath an electric line.  I believe that a small (2V) was being 
> induced into the control wiring and that 2V signal appeard as a closed 
> circuit to the pump controller.  I used the float switch to control an 
> external contactor.  The external contactor switched a short length of wire 
> on the pump controller's dry contactor and that resolved the issue.
> 
> Cordially,
>  Nick Soleil
> Enphase Energy
>  Senior Product Manager
>  (707) 763-4784 x7267  // office
>  (707) 321-2937  // cell
> Powering What’s Next™ | The Enphase Energy Management System
> NABCEP Certified Solar PV Installer #03262011-300
> California C10 Licensed Electrician #986315
>  
> From: RE-wrenches <[email protected]> on behalf of 
> Bob-O <[email protected]>
> Sent: Friday, February 25, 2022 8:21 AM
> To: RE-wrenches <[email protected]>
> Subject: Re: [RE-wrenches] grundfos cu200 failure?
>  
> EXTERNAL EMAIL - Use caution when responding, clicking, and/or downloading 
> attachments.
>  
> 
>  
> 
> Jay, I agree it’s probably a controller failure but double check your float 
> wiring, especially if it’s been in service for awhile. The current required 
> to activate that circuit is minuscule. A little corrosion or a loose 
> connection can make that controller do funny things. 
> 
> Bob-O
> 
> On Feb 24, 2022, at 8:12 PM, Jay <[email protected]> wrote:
> 
> 
> Yes. 
> And if that light is on it’s supposed to stop pumping. Even if the float was 
> bad or maybe the wires were bad, if the cu200 is seeing a full tank signal 
> it’s supposed to shut off the pump. 
> And it’s not. 
> 
> I’ve just never seen this failure mode before. 
> 
> Jay
> 
> 
> 
>> On Feb 24, 2022, at 8:48 PM, Mac Lewis <[email protected]> wrote:
>> 
>> 
>> Hi Jay,
>> 
>> Have you ruled out a problem with the float switch/wiring?
>> 
>> On Thu, Feb 24, 2022 at 5:13 PM jay <[email protected]> wrote:
>> HI All,
>> 
>> Has anyone seen this failure mode on a Grundfos CU200.
>> 
>> The tank full  light is on and it keeps pumping ( green arrows working)
>> 
>> I suspect the CU200 just needs to be replaced, but as they are pretty pricy 
>> I’d thought I’d ask around first.
>> 
>> thanks
>> 
>> jay
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
>> 
>> 
>> -- 
>> 
>> 
>> 
>> Mac Lewis
>> 
>> "Yo solo sé que no sé nada." -Sócrates
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to