Kirpal:

I have used 1000A/100mv shunts connected to an FNDC without issue. As long
as the ratio of A to mv is the same the FNDC will not know the difference.

Am I missing something?

Thanks in advance.

William

On Tue, Mar 1, 2022 at 7:54 AM Kirpal <[email protected]> wrote:

> Kirk.  Good morning.  The 175A breaker assembly is included in the bare
> GSLC box for the radians.  You have to order the 175A breakers separately;
> they are not included.  The bare box includes a 500A 50MV shunt, the
> breaker brackets to connect breakers to the inverter and that's it.  No AC
> buss bars are included.  Negative and ground buss bars are included.
> In a multi inverter system if 1000A 100mv shunt size is needed, note that
> you can not mix 500A and 1000A shunts on a single flexnet DC.  It doesn't
> work.  Shunts all have to be the same.  I found this out the hard way.
>
> Sunny Regards,
> Kirpal Khalsa
> Oregon LRT#25
> Oregon Solarworks LLC
> www.oregonsolarworks.com
> 541-299-0402
>
>
>
>> ________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --

William Miller
Miller Solar.com
895-438-5600
www.millersolar.com
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to