Hiya William,

Does the empty GSLC come with a top, or do you fabricate a top where the Radian 
usually bolts on? Would love to see a picture of your dead front hinge,  I 
always wanted to to that….
Thanks,

Jason Lerner
Waldron Power and Light Co.


> On Mar 1, 2022, at 8:53 AM, William Miller <[email protected]> wrote:
> 
> Kirk:
> 
> We purchase only the empty GSLC cabinets. They do include the breaker 
> brackets and bus bars. I have received the cabinets missing hardware so check 
> the inventory beforehand. 
> 
> Here are a few hints you probably already know:
> 
> The shunts are the shoddiest construction and it is very easy to break the 
> plastic base. Torque the upper shunt bolt after all other bus hardware is 
> torqued. 
> 
> I recommend using two 175A breakers. For some troubleshooting procedures it 
> is necessary to isolate the two power modules. 
> 
> An empty GSLC cabinet makes an acceptable PV recombiner. We cut off the 
> bottom dead front tab and substitute a hinge. We wire the breakers with the 
> dead font tilted out flat and all leads hinging at the bottom. 
> 
> We never install any AC breakers in the GSLC cabinets. The back-wiring is 
> just too awkward. Instead  we use outboard breaker panels or panel boards—one 
> for Gen Fed and one for Inverter Fed.  
> 
> For bypassing we fabricate custom slide plates bolted to the dead-front to 
> interlock output breakers. It’s not listed but with good craftsmanship it 
> looks official. 
> 
> Here are a few photos:
> 
> https://millersolar.com/MillerSolar/Portfolio/Inverters/battery_iinverters/JP_Radian/JP_Radian.html
>  
> <https://millersolar.com/MillerSolar/Portfolio/Inverters/battery_iinverters/JP_Radian/JP_Radian.html>
> 
> I hope the above info is helpful. 
> 
> William Miller
> 
> On Tue, Mar 1, 2022 at 6:23 AM Kirk Herander <[email protected]> wrote:
> All,
> 
> I am doing a multiple stacked Radian GS8048 system. And all I need in my 
> design is two OB 175 a breakers in a box which integrates w/ each respective 
> inverter. The manual bypass switch is useless, for all inverters need to be 
> bypassed at once using a single external bypass. OB does not make a version 
> of the GSLC which only has the inverter breakers. They do make an empty GSLC 
> with nothing in it. But no mounting assembly for the breakers, and no add-on 
> kit offering to do this either.
> I thought Midnite made something compatible, but don't see it on their web 
> site. Any ideas? Thanks.
> 
> -- 
> Kirk Herander /  <>[email protected] <mailto:[email protected]>
> Owner|Principal, VT Solar, LLC
> Celebrating our 31st Anniversary 1991-2022!!
> www.vermont.solar 
> <https://nam02.safelinks.protection.outlook.com/?url=www.vermontsolarnow.com&data=02%7C01%7C%7C9f0330d75a244870112408d685311841%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636842843233477645&sdata=0NjyuKeQbEK6245SNnk8X4XnP9Q%2B%2BqtvcALkdDghvk4%3D&reserved=0>
> dba Vermont Solar Engineering
> 802.863.1202
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org 
> <http://re-wrenches.org/>
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/ 
> <https://www.mail-archive.com/[email protected]/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm 
> <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 
> -- 
> 
> William Miller
> Miller Solar.com
> 895-438-5600
> www.millersolar.com <http://www.millersolar.com/>
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to