That's how I read it. They meant to write:

"UFO and Bonding Hardware must be installed *no less than *1" away from the
point where two Rails join together."

It's frustrating when using 41.5" W modules on 168" IronRidge rails. Four
panels just barely fit on one rail, so when splicing for more modules you
need to cut some rail off.

Jason Szumlanski
Florida Solar Design Group






On Wed, Mar 16, 2022 at 4:08 PM Daniel Young <[email protected]> wrote:

> My read on that is that the splice needs to be anywhere EXCEPT where two
> modules meet, so for every 40” nominal module width, there is a 2”
> exclusion zone (5% of the module width), so there is a 95% chance a random
> splice placement will be in a good place.
>
>
>
> Basically they don’t want mid clamps right on the splice.
>
>
>
> --
>
>
>
> Danny Young
>
> Engineering Team Lead
> Solar Energy Solutions
>
> Lexington | Louisville | Bloomington | Cincinnati | Evansville |
> Indianapolis
>
> 513-448-5176 (mobile)
>
> 877-312-7456 (Main Office)
>
> [email protected]
>
>
>
> *From:* RE-wrenches <[email protected]> *On
> Behalf Of *Dave Tedeyan
> *Sent:* Wednesday, March 16, 2022 3:38 PM
> *To:* RE-wrenches <[email protected]>
> *Subject:* [RE-wrenches] Ironridge BOSS splice
>
>
>
> Hi All,
>
>
>
> I am looking through the installation manual for Ironridge racking and
> noticed this:
>
> --------
>
> BOSS - Bonded Structual Splice
> Insert BOSS into first Rail up until the Stop Tab. Slide second Rail fully
> into place.
> ➢ Rows using Classic Splice or BOSS and exceeding 100 feet of Rail must
> use
> Expansion Joints.
> ➢ Boss Splices may be installed in any location within a span.
> ➢
> *UFO and Bonding Hardware must be installed 1" away from the point where
> two Rails join together.*
>
> *------*
>
> I put the third bullet point in bold. Is this saying that you need to
> ensure that the splice ends up essentially right where two modules meet? Or
> are they talking about for an expansion joint only? Needing to plan out the
> exact splice locations and cut every rail to the right length seems to make
> these splices way more difficult to work with than the normal splice, so I
> don't get why anyone would use them.
>
>
>
> Cheers,
>
> Dave
>
>
>
> --
>
> [image: Logo]
> <https://mailtrack.io/trace/link/4d1996105ba7f47f07eff2417581599d9b254e62?url=https%3A%2F%2Fwww.sungineersolar.com%2F&userId=1613865&signature=646c02ea29544933>
>
>
> *Dave Tedeyan, P.E. Owner | Sungineer Solar*
>
> *p: *he | him | his
> * a: *1653 Slaterville Rd. | Ithaca, NY 14850
> *w:* www.sungineersolar.com
> <https://mailtrack.io/trace/link/69d0e2be7b463666f46256049eb0e2e962ac00c6?url=http%3A%2F%2Fwww.sungineersolar.com%2F&userId=1613865&signature=29437372b0cf8d1c>
> *c:* (607) 288-2898
>
>
> _______________________________________________
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to