Wrenches
The new solark 15 has a 200 amp rated contactor this is so if you want to
have whole home pass through you can but if you only have an inverter then
use that as your starting point and if the genny is contributing then add
that is, you do not need 2/0 for a single 15 k off grid but you may grid
tied. this opens up other issues that are not part of this conversation
like multiple 15 and 3/0 grid tied remember KIS!

On Fri, Apr 15, 2022 at 8:00 AM Jason Szumlanski via RE-wrenches <
[email protected]> wrote:

> I'm not following the wiring diagrams for this new inverter. It has 200A
> pass-through capability with an integrated 200A load disconnect. But then
> it says the wire gauge for the load out wiring can be #4 to 2/0.
>
> In an off-grid scenario where there is no generator, the max continuous
> output is 62.5A, so I assume 80A circuit protection could be used with 80A
> rated wire (#4), but how is that circuit protection implemented if the 200A
> breaker is integrated? Do you have to run a short piece of 2/0 to an
> external 80A rated OCPD and then step down to #4?
>
> Jason Szumlanski
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to