Aloha Chris,

We have numerous Sol-Ark systems with Tigo TS4Fs where we have the transmitter wired to the 12v supply of the inverter, with no issues to date.

Sent from a IPhone, with touch screen keys on the fly. Please excuse shortcuts and typos. 

Roland Shackelford
NABCEP CERTIFIED PV INSTALLER
President 
Renewable Energy Services (RES), Inc. 
Mobile:  808-938-9239

On Nov 16, 2022, at 4:33 AM, Christopher Warfel via RE-wrenches <[email protected]> wrote:



Hi, We are doing our first system with these two devices. The inverter is SolArk 12P (mutimode) and the Tigo product for RS is the TS4F.  Tigo has me a little bit walking in circles.

I told them that SolArk says not to use the 12VDC RS output terminals for connecting the transmitter.  I gave them the attached drawing which they ask for, which shows the transmitter connected to a 120VAC/12VDC breaker which they supply.  They told me to wire the 120VAC source to the main service panel so the array would shut down on loss of power. I told them that is exactly NOTwhat I wanted to happen as that would stop the battery charging when there is a loss of utility power. I said I wanted the 120VAC source to be the back up loads panel. After about a week of calls and emails, I got an email back saying to use the SolArk 12VDC terminals for RS.  I just emailed them a screen shot of the SolArk manual that says not to do that.

At this point, I am asking anyone on the list to let me know how they wired the transmitter successfully. Thank you for any guidance, Chris Warfel





--
                                         Christopher Warfel
                     ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
                                                            401-466-8978



Attachment: Tigo Transmitter Powering.pdf
Description: Adobe PDF document

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to