All, I believe what Chris is referring to is something I was initially confused on during a Solark install I was involved with last year. Uncertain if the manual has changed but in the Solark 12k manual dated April 2, 2021 on page 23 it has a line saying-
Note: Tigo Optimizers are compatible with the Sol-Ark 12k (Do not use the built in 12v Power supply in the Sol-Ark user area to power the Tigo Optimizer TX transmitter) I too had to confirm with Sol-Ark to clarify these details. I’ve not looked at any of their newer manuals to see if some of these notes have changed. Enjoy your day, Nick > On Nov 16, 2022, at 8:41 AM, Chris Sparadeo via RE-wrenches > <[email protected]> wrote: > > Hi Chris, > > I echo Ronald’s experience. I wasn’t aware of any memo from Sol Ark > suggesting pins 15 and 16 should not be used for the Tigo RSS Transmitter. > The 12K and 15K manuals both refrence a 12vdc RSS transmitter to achieve > rapid shut down. > > Best, > > Chris > > On Wed, Nov 16, 2022 at 11:21 AM Roland - RES via RE-wrenches > <[email protected] > <mailto:[email protected]>> wrote: > Aloha Chris, > > We have numerous Sol-Ark systems with Tigo TS4Fs where we have the > transmitter wired to the 12v supply of the inverter, with no issues to date. > >> Sent from a IPhone, with touch screen keys on the fly. Please excuse >> shortcuts and typos. >> > Roland Shackelford > NABCEP CERTIFIED PV INSTALLER > President > Renewable Energy Services (RES), Inc. > Mobile: 808-938-9239 <http://808-938-9239/> > www.renewablenergy.com <http://www.renewablenergy.com/> > >> On Nov 16, 2022, at 4:33 AM, Christopher Warfel via RE-wrenches >> <[email protected] >> <mailto:[email protected]>> wrote: >> >> > >> Hi, We are doing our first system with these two devices. The inverter is >> SolArk 12P (mutimode) and the Tigo product for RS is the TS4F. Tigo has me >> a little bit walking in circles. >> >> I told them that SolArk says not to use the 12VDC RS output terminals for >> connecting the transmitter. I gave them the attached drawing which they ask >> for, which shows the transmitter connected to a 120VAC/12VDC breaker which >> they supply. They told me to wire the 120VAC source to the main service >> panel so the array would shut down on loss of power. I told them that is >> exactly NOTwhat I wanted to happen as that would stop the battery charging >> when there is a loss of utility power. I said I wanted the 120VAC source to >> be the back up loads panel. After about a week of calls and emails, I got an >> email back saying to use the SolArk 12VDC terminals for RS. I just emailed >> them a screen shot of the SolArk manual that says not to do that. >> >> At this point, I am asking anyone on the list to let me know how they wired >> the transmitter successfully. Thank you for any guidance, Chris Warfel >> >> >> >> >> >> >> >> >> >> -- >> Christopher Warfel >> ENTECH Engineering, Inc. >> PO Box 871, Block Island, RI 02807 >> 401-466-8978 >> <http://entech-engineering.com/> >> <http://entech-engineering.com/> >> >> > >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> Pay optional member dues here: http://re-wrenches.org >> <http://re-wrenches.org/> >> >> List Address: [email protected] >> <mailto:[email protected]> >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> >> >> There are two list archives for searching. When one doesn't work, try the >> other: >> https://www.mail-archive.com/[email protected]/ >> <https://www.mail-archive.com/[email protected]/> >> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org >> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> >> >> List rules & etiquette: >> http://www.re-wrenches.org/etiquette.htm >> <http://www.re-wrenches.org/etiquette.htm> >> >> Check out or update participant bios: >> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/> >> > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > <http://re-wrenches.org/> > > List Address: [email protected] > <mailto:[email protected]> > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > <https://www.mail-archive.com/[email protected]/> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > <http://www.re-wrenches.org/etiquette.htm> > > Check out or update participant bios: > http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/> > > -- > Chris Sparadeo > > > C_802-369-4458 > H_802-728-3059 > _______________________________________________ > List sponsored by Redwood Alliance > > Pay optional member dues here: http://re-wrenches.org > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > There are two list archives for searching. When one doesn't work, try the > other: > https://www.mail-archive.com/[email protected]/ > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org > > List rules & etiquette: > http://www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > http://www.members.re-wrenches.org >
_______________________________________________ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org There are two list archives for searching. When one doesn't work, try the other: https://www.mail-archive.com/[email protected]/ http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: http://www.re-wrenches.org/etiquette.htm Check out or update participant bios: http://www.members.re-wrenches.org