Wrenches and Ray
So did you properly configuer the master slave battery config, I have
several set up with no issues SOC is within1 to 2% and volatge is the same,
what inverter/chargers are you using are you still connnected to bat temp
sensors I assume there is no connection to the inverter(s)
Jerry

On Wed, Nov 16, 2022 at 11:02 AM Ray Walters via RE-wrenches <
[email protected]> wrote:

> Greetings Fellow Wrenches;
>
> Based on glowing reports from the RE list, I finally used Fortress for a
> battery replacement for a long time customer. Overall, it seems to be a
> better solution than others I've seen. However, we are having issues.
> First the two batteries are supposed to be linked together in a master/
> slave configuration, but they charge and discharge unevenly, and have
> SOC often 20% different.   Batteries are connected to a common buss with
> equal length 4/0 cables.
>
> I've been truly disappointed with Fortress customer support. First, I've
> called multiple times over the past two weeks, and never got through to
> anyone.  Their online support system is quite flawed as well, and I had
> a very difficult time even setting up a support ticket.  Now I can't
> even log in to view the support ticket, and I've only received one email
> back asking if I had properly paralleled the batteries.
>
> Has anyone else had a hard time with Fortress support?  Does anyone have
> a direct contact?  Customer is beyond pissed now, after almost 2 weeks
> hearing nothing, and having spent tens of thousands.
>
> Thanks;
>
> Ray Walters
> Remote Solar
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to