Howie,
Just to add, I have noticed this type of behavior with a Solark system with AGM
batteries. It was very clear that the Solark was limiting the charge to the
batteries (about 35-40AmpsDC) when the generator was running, but not clear as
to why. This happened after a recent firmware update (maybe 2 months ago) on a
Solark 12K Outdoor. The Solark tech looks things over, Enabled the “Activate
Battery” setting (I do not know what this does), and he may have changed
something else but I don’t think so. Anyways after that it started charging at
a higher rate again and I believe has been good since.
We also have had some ongoing trouble with the Generator turning on and turning
off when it’s supposed to…and wishing their was more customization with the Gen
settings, as I know others have mentioned before.
Best,
Amos
Amos Post
Integrity Energy
W 802.763.7023
C 802.291.2188
ienergyVT.com <http://www.ienergyvt.com/>
Facebook <https://www.facebook.com/integrityenergyllp?ref=hl>
> On Nov 17, 2022, at 5:36 PM, Jerry Shafer via RE-wrenches
> <[email protected]> wrote:
>
> Wrenches, Howie
> As SOC climbs the rate of current will reduce current flow, what was the SOC
> when you had both connected and configured master slave with in the batteries
> Fun times
>
> On Wed, Nov 16, 2022 at 9:59 PM Howie Michaelson via RE-wrenches
> <[email protected]
> <mailto:[email protected]>> wrote:
> Good Evening,
>
> I have a frustrating charging issue involving 2 Fortress eVault Maxs
> connected to a Sol-Ark 15k. Commissioned the system last week, replacing a
> legacy off-grid Dual Stack SunnyIsland 5048s and 2-volt Rolls battery system.
> Initially, we connected one of the eVaults to the Sol-Ark, programmed it to
> Fortress' and Sol-Ark's specs, setup closed loop, and things seemed fine.
> The battery charged at around 95 amps off the 20kW Kohler. The next day we
> connected the 2nd eVault, went through the procedures as Fortress suggested,
> made the necessary settings changes in the Sol-Ark, and that is when the
> issue started.
>
> Ever since we connected the 2nd eVault, we have not been able to get the
> charge rate much above a combined total of 35 amps. Fortress has pretty much
> said that it can't be anything on their end (although the communication with
> them has been very much limited and frustrating). They say that nothing on
> their side would limit the charge rate to that low, especially if the
> batteries were in a lower state of charge. We've talked to at least 3
> different Sol-Ark technicians more than once. We have changed the setting
> between closed loop, % SOC, and Battery Voltage multiple times. We've tried
> dropping back to a single battery, both the first one we had connected and
> the second one (changing the battery setup and the Sol-Ark parameters, but
> have only seen at times a moderate increase in maximum charge rate (up to
> about 40 amps total).
>
> This small increase happened after a Fortress technician suggested that we
> turn on both the generator and the grid charging toggles (the generator is
> connected to the grid port on the Sol-Ark as per Sol-Ark's recommendation.
> Sol-Ark has run out of suggestions at the moment, and are having us cycle the
> batteries tonight and they will start another charge cycle in the morning to
> see if having a lower SOC along with the firmware reload will change anyhing
> (I don't think it will - it didn't the last several times.
>
> Has anybody seen this type of behavior before? I don't think it is a
> settings issue, as several technicians have gone through them, I have gone
> over them many times using the Fortress/Sol-Ark integration white papers.
> Hoping to get higher level tech involved ASAP, since I don't feel like the
> lower level techs know enough to provide useful ideas.
>
> Thanks,
> Howie
> Howie Michaelson
> Sun Catcher
> NABCEP Certified Solar PV Installer™
>
> Solar Electric Systems Sales & Service
> 802-272-0004
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
> <http://re-wrenches.org/>
>
> List Address: [email protected]
> <mailto:[email protected]>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> <https://www.mail-archive.com/[email protected]/>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org