Larry.

Hera's an idea. Put a 1:1 isolation transformer of suitable power rating between the inverter and load. The iron core will act as a energy storage element allowing for a cleaner ac waveform during start.


Frank BZP



On 1/13/2023 12:54 PM, Starlight via RE-wrenches wrote:
Any new AC equipment connected and running during test? Scope the waveform during equipment start to see if the distortion is severe. I have seen a 300W load make a mess of a Magnum AC waveform.

Larry Crutcher
Starlight Solar Power Systems



On Jan 13, 2023, at 11:48 AM, Mac Lewis <[email protected]> wrote:

Good question Larry,

Rock solid 52V on a lithium battery system. Doesn't appear to be a battery problem at all.

On Fri, Jan 13, 2023, 11:41 AM Starlight <[email protected]> wrote:

    Mac,

    What was the lowest voltage measured at inverter battery terminals
    during the inrush measurement?

    Larry Crutcher
    Starlight Solar Power Systems



    On Jan 13, 2023, at 11:33 AM, Mac Lewis via RE-wrenches
    <[email protected]> wrote:

    Hello Wrenches,

    I have a new client that has ran a pretty decent wood shop for
    about 10 years on a Magnum 4448.  He's got some large loads,
    planers, saws, compressors vacuums etc.  They are really nice,
    heavy duty pieces of equipment.  Amazingly, the Magnum has been
    able to start these loads for the most part for 10 years, but he
    has reported that it has gotten worse lately (could be a load
    issue), brown outs, dimming etc

    He wants to upgrade the system, get remote monitoring etc.  I
    tried a test with a Sol-Ark 12, and it won't start these large
    motor loads.  I was a little surprised by that but I know they
    aren't as good as the low freq transformer based inverters at
    these surges.

    I confirmed that its not just an overload from imbalance because
    the 240V loads will also overload it.  I got an inrush measurement
    of 48.5A Ac @240 (but it didn't start the load before Sol-Ark
    would shut off)

    What are my options?
    Schneider XW Pro 6848
    Outback Radian 8048 (Is this a low freq device?)
    Sunny Islands are beasts but weird to work with and not user friendly

    Any others I should consider?  He does have some significant 120
    only loads so I don't think the Outback vfxr are a good choice.

    Is it as simple as saying if the Magnum can start this load, the
    Radian should?

    I appreciate your input!

    --
    Mac Lewis

    *


    *
    _______________________________________________


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to