In high uplift scenarios, I have used both IronRidge Camo clips on the
bottom frame of the module and UFO clips on the top. More expensive, but
definitely an all around rock solid approach.

-Chris

On Thu, Mar 30, 2023 at 9:45 PM Ray Walters via RE-wrenches <
[email protected]> wrote:

> Hi Jason;
>
> I was like you: thinking good ol' bottom mounting with SS hardware was the
> best.  All of us old wrenches were wrong.
>
> The top down mounting system is much stronger.  I've only had a handful of
> failures over 25 years, and all were bottom mounted.  The module completely
> ripped off the rack, leaving the stainless hardware, washers, etc with a
> thin sliver of module frame between.  For repairs, I come back and install
> 1/2" SS angle on the inside of the module frame to spread the load more.
> AND....on new installs, no more bottom mounting. If you compare today's
> modules with old 12v models from 20 years ago, you'll see: much thinner
> metal on the bottom frames now.
>
> Meanwhile I saw several systems survive Hurricane Maria in Puerto Rico:
> all top down mounting.  You are correct that the failures come from the
> modules themselves letting go, not the racking.  Either the wind itself is
> so strong as to blow the glass, then the frame looses its structure, or
> flying debris breaks the glass. There were some MW PV fields that got tore
> up pretty bad.  So no, ground mounts definitely can be destroyed. They had
> tornadoes moving inside of the hurricane, and you could see it in the
> damage, 50' wide strips of total carnage with undamaged modules a few feet
> away. Like you said, The storm has a mind of its own.
>
> As far as mid clamp T bolt failures, I can confirm that probably a
> majority are not installed correctly, especially Unirac, which are terrible
> to get the T lined up right.  I've done numerous inspections world wide,
> and a signifcant % of racking I looked at was NOT installed correctly.
> 1) The Ts not squarely lined up with the rail,
> 2) massive over torqueing, to the point the bolt can't be reversed
> 3)  under torqueing, to the point the modules had slipped down a little.
>
> Most of these problems come from installing with an impact driver.  Impact
> drivers are a great tool (so is a hammer), but you got to know when and
> where to Not use them, too.  They're great for installing the lags and L
> feet, but then get that tool off the roof.
>
> Use an electric screw driver, socket wrench, or *drill with a clutch* set
> low to snug up the clamps, and then final torque with a torque wrench.
> Period.
>
> Ray Walters
> Remote Solar
> Former NABCEP 2004-2016
>
>
> On 3/30/2023 4:34 PM, Jason Szumlanski via RE-wrenches wrote:
>
> That would be great if it were possible! I'm not sure how you bottom mount
> a flush mount array. For a brief period many years ago, I was building
> solar trailers. I would bottom mount 4-6 panel arrays on rails in my
> warehouse and then hoist them up and through-bolt the whole array on the
> top of a trailer. I wasn't about to allow a trailer going 80 mph on the
> interstate to have panels mounted on the roof with mid-clamps! I had no
> idea what I was doing, but I had enough sense to know that would have been
> a bad idea!
>
> I did provide feedback to IronRidge regarding a handful of failures from
> Hurricane Ian, but most of the issues we saw were most likely related to
> catastrophic module failure. After all, they are only tested to 5600 Pa
> uplift for even the best options we have on the market and 2400 Pa for some
> (which I refuse to use). The mid-clamp T-bolts tearing out of the rail are
> slightly concerning, but this was pretty rare, and honestly it could be
> related to installation torque issues, misalignment, or coupled with module
> failure. There was no widespread or definitive reason for rail failures at
> the clamp locations.
>
> I would suggest that FEMA's recommendation is overkill and not based on
> much science, but conclusions based on anecdotal information without
> statistical data. It should be scrutinized. I think it would be a good idea
> to consider bottom mount for ground racks and tilt mounts that allow it,
> but it's just not practical or possible in the vast majority of residential
> installation cases. On that note, I am not aware of any ground mount
> failures around here from Hurricane Ian except for submerged arrays that
> were washed away from storm surge (Yikes!). And the handful of failures
> that we observed were a drop in the bucket relative to the installed
> numbers here.
>
> One other thing. Wind direction, upwind obstructions/windbreaks, and luck
> have a huge amount to do with failures (of both PV and roofs themselves).
> These storms pick winners and losers. You will have ten houses in a row
> with pool enclosures mangled, and one in the middle that is unscathed. It's
> crazy to see. We have lots of gated communities with houses close together.
> When wind accelerates between houses, it can topple air conditioning units
> and pool equipment. If you look hard enough at where the wind was coming
> from and the surrounding area, you can really see how there are so many
> factors that come into play.
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
>
>
> On Thu, Mar 30, 2023 at 7:35 AM Christopher Warfel via RE-wrenches <
> [email protected]> wrote:
>
>> If you look at FEMA's design guide for solar installations in FL and the
>> Caribbean, the recommended module to rail attachment method is back to
>> using the attachment holes in the solar module.  Chris
>> On 3/30/2023 5:56 AM, Jason Szumlanski via RE-wrenches wrote:
>>
>> This thread has morphed into more than it started as, and for good
>> reason. I want to provide some practical/anecdotal information, having just
>> gone through arguably the most catastrophic wind event in Florida's history
>> (Ian) since the boom in solar energy started, and another major wind event
>> (Irrma) just 5 years ago.
>>
>> First, Aside from the Sunmodo and Quickbolt decking-only products, I
>> would check out IronRidge's new entrant into the market, the IronRidge HUG.
>> If you can't find info on it, ask your distributor or IronRidge sales rep.
>> They have data on truss attachments and also missed truss installation
>> procedures. It's a unique approach to a dual-purpose product, and they did
>> a stellar job on the engineering documentation in my opinion.
>>
>> Ok, now let's get to my most important point. Due to Hurricane Ian, the
>> number of roofing PV attachments that I have witnessed that failed due to
>> fastener pull-out (mine or competitors):
>>
>> ZERO
>>
>> The only building where we had any mounts fail was on a flat roof with
>> pitched panels and Anchor Products mounts on TPO membrane, but the mounts
>> themselves did not cause the failure. The roofing system itself failed,
>> causing a small section of the PV system to fail. But even in that case,
>> the following applies...
>>
>> The weak point in a well-designed and installed system is not the
>> fastener or flashing system. The module to rail connection is where we saw
>> failures. These failures fell into a few categories:
>>
>>    - Windborne debris struck panel, panel frame failed, panel popped out
>>    of mid-clamps.
>>    - Catastrophic wind forces popped panels out of mid-clamps (a good
>>    percentage of panels found INTACT and still functional on the ground!) I
>>    suspect the panels became covex in the wind, bending frames inward.
>>    - Windborne debris struck mounting system components, panel
>>    dislodged, often still on the roof suspended by DC leads.
>>    - Mid-clamp t-bolt tore out of aluminum rail channel (IronRidge UFO,
>>    Unirac SM).
>>    - Mid-clamp sheared off (Quick Mount QRail).
>>    - Unexplained module detachment failures.
>>
>> On 9/28/22, while I stayed up all night bracing myself against my front
>> door that I thought was about to fail, I was imagining how many roof leaks
>> my clients were about to endure, and wondered about the efficacy of my
>> business going forward. Those fears never materialized. Aside from a
>> handful of minor panel dislodgements, there was no panic following the
>> storm (with respect to solar panels). The bigger problem became all of the
>> people needing to remove panels for roof replacements, but PV panels
>> largely protected roofs in the areas where they were installed. Sadly, the
>> rest of the roof often did not fare as well.
>>
>> Anyway, back to the decking attachments. I have been skeptical of
>> non-flashed products for comp shingle roofs for a long time. My thinking is
>> coming around, particularly with the HUG (I trust IronRidge's testing
>> regime). And sealants have come so far. This method will remain up for
>> debate probably for a long time. Around here, I am pretty certain these
>> products will outlast the shingles they are placed upon. We only get 15
>> years out of most shingle roofs around here.
>>
>> About the pull-out fears... Mine are gone. We have done many flat roofs
>> with long fasteners through steel decking or wood decking. These screws are
>> usually something like #15 XHD screws in lengths from 5 - 12". Not a single
>> failure. We have also used Quick Mount QBase Low-Slope bases on pitched
>> tile roofs that were only screwed into decking with 4 fasteners each (due
>> to horizontal truss transitions) in some cases. Zero failures. But the most
>> relevant attachments I can think of that are germane to this discussion are
>> the many thousands of S-5 SolarFoot that we have screwed into decking on 5V
>> metal roofs around here. These have four screws per attachment, and S-5
>> load tests show something like 240 lbs of pull-out strength in OSB
>> (adjusted for safety factor). When engineered for our wind loads, we
>> usually get anywhere from 36-48 inch attachment spacing, sometimes 24
>> inches in certain roof zones. Again, not a single failure.
>>
>> I have more solar installations on Sanibel Island and Fort Myers Beach
>> (Hurricane Ian Ground zero) than anyone. Many of those have decking-only
>> attachments, S-5 clamps, flat roofs, or other attachments other than
>> trusses. I can tell you unequivocally that I trust decking-only attachments
>> from a pull-out strength standpoint. When properly engineered, with
>> cautious attachment spacing, these mounts work in both OSB and plywood.
>> Because of the inconsistencies in OSB, we always err on the side of
>> caution, if not in the engineering, then in the installation, by installing
>> more attachments than prescribed. But the evidence is clear. It works.
>>
>>
>> Caveat to the above: I have zero experience with snow or seismic, and no
>> experience on roofs exceeding 8:12 pitch, and few above 6:12.
>>
>> And one more shout-out to S-5 clamps on standing seam roofs. Aside from
>> one minor failure of the roof metal itself, not an S-5 failure, we had zero
>> failures of S-5 clamps attachments to report.
>>
>> I hope this anecdotal information helps and sets some fears aside. Please
>> reach out to me off-list if you want any specifics or details about our
>> experience with catastrophic wind events.
>>
>> Sincerely,
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>>
>>
>> On Thu, Mar 30, 2023 at 2:47 AM William Miller via RE-wrenches <
>> [email protected]> wrote:
>>
>>> Friends:
>>>
>>>
>>>
>>> Thanks for bringing up this scenario.
>>>
>>>
>>>
>>> I have two problems with using a product such as the easy-feet or other
>>> deck-fastened brackets, particularly on a rigid foam-above-sheeting roof:
>>>
>>>
>>>
>>> 1.   I worry about compression of the foam material over time.  This
>>> could leave a void under the bracket which could lead to leaks or wobbly
>>> brackets.
>>>
>>> 2.   I don’t believe in chemical solutions for sloped-roof
>>> rain-proofing.  By that I mean the use of caulks, gaskets, etc.  Since
>>> roofs were first thatched, the overriding wisdom is that gravity is the
>>> only way to reliably shed water.  Overlapping, seamless material is the
>>> only method to use.  Caulks degrade, roof surfaces become powdery, and the
>>> rafter is often under an architectural feature or seam in the shingles.
>>>
>>> I researched the PLP EZ foot back when the company was DPW.  The
>>> fasteners provided were not rated for the application, according to the
>>> fastener manufacturer.  If you can match the fasteners to the decking and
>>> the forces, then maybe you have a start to a mounting solution.
>>>
>>>
>>>
>>> Whatever product you use, I would install it on a section of flashing
>>> metal, lapped under the next course up.  The flashing gives a flat,
>>> seamless surface to caulk or gasket to.  The thicker and wider the
>>> flashing, the more you distribute the downward force
>>>
>>> applied to the bracket by weight and fasteners.  Any voids under the
>>> bracket will have an overlapped flashing above it.
>>>
>>>
>>>
>>> I hope these musings help you find a solution.
>>>
>>>
>>>
>>> William Miller
>>>
>>>
>>>
>>> PS:  I have encountered this roof configuration a few times on flat, 
>>> built-up
>>> roofing (BUR <https://homeinspectioninsider.com/built-up-roofing/>).
>>> We have dealt with it by cutting through the foam, installing blocking on
>>> top of the sheeting and having a roofer feather the blocks into the roofing
>>> with cant strips
>>> <https://www.blueridgefiberboard.com/cant-strip-tapered-edge-smoothes-roof-drainage-slope/>.
>>> A pitched roof is a different situation, however.
>>>
>>>
>>>
>>> Wm
>>>
>>>
>>>
>>> Miller Solar
>>>
>>> 17395 Oak Road, Atascadero, CA 93422
>>>
>>> 805-438-5600
>>>
>>> www.millersolar.com
>>>
>>> CA Lic. 773985
>>>
>>>
>>>
>>>
>>>
>>> *From:* RE-wrenches [mailto:[email protected]] *On
>>> Behalf Of *August Goers via RE-wrenches
>>> *Sent:* Wednesday, March 29, 2023 11:47 AM
>>> *To:* RE-wrenches
>>> *Cc:* August Goers
>>> *Subject:* Re: [RE-wrenches] Attaching Array To or Through Ply
>>>
>>>
>>>
>>> We've found that in the Bay Area that deck-mount solutions typically
>>> pencil out structurally (via a structural professional engineer) as long as
>>> the deck is 1/2" plywood or thicker, assuming we have all the info on how
>>> the roof is constructed. The big assumption is that we can get all that
>>> roof construction info, which can be difficult for existing structures.
>>>
>>>
>>>
>>> We haven't taken the plunge yet on the flahingless deck mount products
>>> like the Sunmodo Nanomount or Unirac Flashloc Duo. I do think that they
>>> offer several significant advantages including not needing to find rafters,
>>> thus virtually eliminating missed pilot holes, and not disturbing the comp
>>> shingle by eliminating prying up the courses to insert the flashing.
>>>
>>>
>>>
>>> August
>>>
>>> Luminalt
>>>
>>>
>>>
>>> On Wed, Mar 29, 2023 at 11:34 AM Solar Energy Solutions via RE-wrenches <
>>> [email protected]> wrote:
>>>
>>> We like Spider Rax… with the flashing!
>>>
>>>
>>>
>>> *Spider-Rax PV Solar Mounting <https://spiderrax.com/>*
>>>
>>> *spiderrax.com <https://spiderrax.com/>*
>>>
>>> *Error! Filename not specified.* <https://spiderrax.com/>
>>>
>>>
>>>
>>> *Andrew Koyaanisqatsi*
>>>
>>> President
>>>
>>>
>>> *Solar Energy Solutions, Inc. The BRIGHT CHOICE*
>>>
>>>
>>>
>>> *Since 1987, helping you and your *
>>>
>>> *Portland neighbors move towards an environmentally sustainable future.*
>>>
>>>
>>>
>>>
>>> *503-238-4502 <503-238-4502> www.SolarEnergyOregon.com
>>> <http://www.solarenergyoregon.com/>*
>>>
>>>
>>>
>>> On Mar 29, 2023, at 11:04 AM, Jerry Shafer via RE-wrenches <
>>> [email protected]> wrote:
>>>
>>> 
>>>
>>> Wrenches
>>>
>>> Sounds like a SIP's type product, there are quite a few multi hole
>>> attachment bases that are designed for SIP's. Most will have a larger base,
>>> lots of holes for screws to attach that do not require rafters underneath
>>> to attach.
>>>
>>> Fun times
>>>
>>>
>>>
>>> On Wed, Mar 29, 2023, 8:30 AM frenergy via RE-wrenches <
>>> [email protected]> wrote:
>>>
>>> Matt,
>>>
>>>             I guess my questions are 1/2" plywood or 5/8" and how thick
>>> is the foam?  Oh and I assume its nominal 2X6 T&G?  Do you know how the
>>> plywood is attached?.....through the foam into the T&G?... to stringers,
>>> nailers or whatever they're called?
>>>
>>> Bill
>>>
>>> Feather River Solar Electric
>>>
>>> Bill Battagin, Owner
>>>
>>> 4291 Nelson St.(shipping)
>>>
>>> 5575 Genesee Rd 
>>> <https://www.google.com/maps/search/5575+Genesee+Rd?entry=gmail&source=g>. 
>>> (USPS, UPS)
>>>
>>> Taylorsville, CA 95983
>>>
>>> 530.284.1925 Office/ 530.258.1641 Cell
>>>
>>> CA Lic 874049
>>>
>>> Solar powered since 1982
>>>
>>> On 3/29/2023 7:53 AM, Dave Tedeyan via RE-wrenches wrote:
>>>
>>> Hi Matt,
>>>
>>> I've used these in the past when on a comp roof and there was no good
>>> way to get into the rafters (or TJI's in this case)
>>>
>>> https://sunmodo.com/nanomount/
>>>
>>>
>>>
>>> You might want to replace the screws with something shorter and beefier
>>> though to get more grip if you are only going into 1/2" plywood.
>>>
>>>
>>>
>>> Cheers,
>>>
>>> Dave
>>>
>>>
>>>
>>> On Wed, Mar 29, 2023 at 10:38 AM Matt Sherald via RE-wrenches <
>>> [email protected]> wrote:
>>>
>>> Hi All,
>>>
>>>
>>>
>>> I've run into a roof-mounted job where the roof is built-up with the
>>> following:
>>>
>>>
>>>
>>> Comp shingle
>>>
>>> Plywood
>>>
>>> Foam board
>>>
>>> T&G (roof deck, but also interior ceiling)
>>>
>>>
>>>
>>> The beams that hold the t&g up are wide-spaced and not convenient for
>>> fastening the full extent of the array.
>>>
>>>
>>>
>>> This being the case, I was considering other fastening options and am
>>> writing to pick the collective brain of the Wrenches to see how others have
>>> addressed similar situations.
>>>
>>>
>>>
>>> One thought I had was to use the PLP Easy Mounting Foot and I'd be glad
>>> for any opinions on that or another solution.
>>>
>>>
>>>
>>> -Matt
>>>
>>>
>>> --
>>>
>>> Matt Sherald
>>>
>>> PIMBY Energy, LLC
>>>
>>> 304-704-5943
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>>
>>>
>> _______________________________________________
>>
>>
>> --
>>                                          Christopher Warfel
>>                      ENTECH Engineering, Inc.
>> PO Box 871, Block Island, RI 02807
>>                                                             401-466-8978
>> <http://entech-engineering.com>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & 
> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the 
> other:https://www.mail-archive.com/[email protected]/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> --
Chris Sparadeo


C_802-369-4458
H_802-728-3059
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to