The SPD was on one of the PV inputs before it came into the house.  There were two Classics, each fed with its own PV input and SPD.  It actually caused an underground splice to fail (high resistance) which I replaced the splice and restored full voltage, and both Classics were working fine.  Just seems unlikely ( but not impossible) that the surge would make it past the Classic without damage, but then damage the Fortress BMS in an otherwise imperceptible manner.   That is our current best theory at the moment though.   I added an SPD on the 48 v buss, before this latest total shutdown.

Ray Walters

On 8/27/2024 2:35 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote:
When I have had someone lose an SPD (I assume it was on DC buss) there is often latent damage (shows up later) to many of the devices.  In a Hi Rel mode, it is recommended to replace it all. Most offgrid is not that critical but try telling that to someone with rotten food. The freezers and reefers are often full of spoils that smells never go away. YUK ! *Dave Angelini Offgrid Solar "we go where powerlines don't" <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/><http://members.sti.net/offgridsolar/> e-mail [email protected] text 209 813 0060*


On 2024-08-27 1:02 pm, Ray Walters via RE-wrenches wrote:

Greetings All;

I have Fortress Battery installation with a pair of E Vault batteries set up in a Master/ Slave arrangement.  Its been working fine for over a year, but the customer just had a complete shutdown of the batteries which left multiple freezers, and refrigerator with rotting food.   When he rebooted the batteries by turning on/off the main breaker on each, they both come up and showed 100% SOC on the Master, and 98% on the other.    There were no fault codes.   I just recently installed a larger PV array, and so the system has been reaching full charge every morning.

I have multiple calls in to Fortress, but not hearing anything back from them at all.  We did have a lightning surge event a few months ago, that damaged a Midnite SPD (first ever for me), and took out the control board on the generator.  One VFX inverter has an LED out, but we only use two inverters of the Quad stack, so I just switched to another inverter.  All other equipment appeared fine: Midnite controllers, rest of the Outback VFX quad stack, and never any issues seen with the Fortress batteries.

The other odd thing, is since he rebooted the batteries, the system is working fine, and recharging to 100%  by 9:30 am as before.    Is it possible the Fortress BMS were damaged and are now having an intermittent shutdown issue?  I did ask him to temporarily disconnect the comms between batteries, in case it is a bad BMS on one, it will isolate it from the other.

This is a tough one to figure out, since it hasn't happened again, and there are no fault codes.  The Mate 3 shows a low frequency AC code, but that's usually just from the generator shutting down.    Any help, ideas, experiences, would be greatly appreciated.

Thanks,

Ray Walters
Remote Solar

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here:http://re-wrenches.org

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to