I have a buddy in tech support at Fortress.

I asked him and he said that elevated absorb volts above 55.2 could cause this 
situation.  
And then the power cycle would reboot the BMS.

I am presuming its open loop, and the fact you mentioned that there was more PV 
and then the shut down sure might be connected.  
You might check the charge voltages/time to make sure they are correct and I 
can’t remember if the classic has battery sense wire connections. 

jay







> On Aug 27, 2024, at 2:51 PM, Ray Walters via RE-wrenches 
> <[email protected]> wrote:
> 
> The SPD was on one of the PV inputs before it came into the house.  There 
> were two Classics, each fed with its own PV input and SPD.  It actually 
> caused an underground splice to fail (high resistance) which I replaced the 
> splice and restored full voltage, and both Classics were working fine.  Just 
> seems unlikely ( but not impossible) that the surge would make it past the 
> Classic without damage, but then damage the Fortress BMS in an otherwise 
> imperceptible manner.   That is our current best theory at the moment though. 
>   I added an SPD on the 48 v buss, before this latest total shutdown.    
> 
> Ray Walters
> 
> On 8/27/2024 2:35 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote:
>> When I have had someone lose an SPD (I assume it was on DC buss) there is 
>> often latent damage (shows up later) to many of the devices.  In a Hi Rel 
>> mode, it is recommended to replace it all. Most offgrid is not that critical 
>> but try telling that to someone with rotten food.
>>  
>> The freezers and reefers are often full of spoils that smells never go away. 
>> YUK !
>>  
>> Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>>    <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ 
>> <https://offgridsolar1.com/>  <http://members.sti.net/offgridsolar/>
>> e-mail  [email protected] <mailto:[email protected]>
>> text 209 813 0060
>> 
>> 
>> On 2024-08-27 1:02 pm, Ray Walters via RE-wrenches wrote:
>> 
>>> Greetings All;
>>> 
>>> I have Fortress Battery installation with a pair of E Vault batteries set 
>>> up in a Master/ Slave arrangement.  Its been working fine for over a year, 
>>> but the customer just had a complete shutdown of the batteries which left 
>>> multiple freezers, and refrigerator with rotting food.   When he rebooted 
>>> the batteries by turning on/off the main breaker on each, they both come up 
>>> and showed 100% SOC on the Master, and 98% on the other.    There were no 
>>> fault codes.   I just recently installed a larger PV array, and so the 
>>> system has been reaching full charge every morning.
>>> 
>>> I have multiple calls in to Fortress, but not hearing anything back from 
>>> them at all.  We did have a lightning surge event a few months ago, that 
>>> damaged a Midnite SPD (first ever for me), and took out the control board 
>>> on the generator.  One VFX inverter has an LED out, but we only use two 
>>> inverters of the Quad stack, so I just switched to another inverter.  All 
>>> other equipment appeared fine: Midnite controllers, rest of the Outback VFX 
>>> quad stack, and never any issues seen with the Fortress batteries.
>>> 
>>> The other odd thing, is since he rebooted the batteries, the system is 
>>> working fine, and recharging to 100%  by 9:30 am as before.    Is it 
>>> possible the Fortress BMS were damaged and are now having an intermittent 
>>> shutdown issue?  I did ask him to temporarily disconnect the comms between 
>>> batteries, in case it is a bad BMS on one, it will isolate it from the 
>>> other.
>>> 
>>> This is a tough one to figure out, since it hasn't happened again, and 
>>> there are no fault codes.  The Mate 3 shows a low frequency AC code, but 
>>> that's usually just from the generator shutting down.    Any help, ideas, 
>>> experiences, would be greatly appreciated.
>>> 
>>> Thanks,
>>> 
>>> Ray Walters
>>> Remote Solar
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org 
>>> <http://re-wrenches.org/>
>>> 
>>> List Address: [email protected] 
>>> <mailto:[email protected]>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>> 
>>> There are two list archives for searching. When one doesn't work, try the 
>>> other:
>>> https://www.mail-archive.com/[email protected]/ 
>>> <https://www.mail-archive.com/[email protected]/>
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm 
>>> <http://www.re-wrenches.org/etiquette.htm>
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org 
>> <http://re-wrenches.org/>
>> 
>> List Address: [email protected] 
>> <mailto:[email protected]>
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>> 
>> There are two list archives for searching. When one doesn't work, try the 
>> other:
>> https://www.mail-archive.com/[email protected]/ 
>> <https://www.mail-archive.com/[email protected]/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org 
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm 
>> <http://www.re-wrenches.org/etiquette.htm>
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the 
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to