Answering the question, for the archives:

Google "AI" found me a phone number 219-734-5500 which got me to a live
Fronius tech support person in well less than a minute. This number doesn't
appear to be on their website. Tech support definitively answered that no
neutral is required and that is perfectly fine to configure the inverter
for "delta" when connected to wye without a neutral present. She said there
is no downside to it. She did say that a neutral is required for the 480
volt Symo inverters.

Electrically this all is as I expected. This saves well over a thousand
dollars of conduit and conductor.


-James Jefferson Jarvis
APRS World, LLC
+1-507-454-2727
http://www.aprsworld.com/


On Tue, Nov 5, 2024 at 8:47 AM James Jarvis <[email protected]> wrote:

> Hi Group,
>
> We have an install with four Fronius Symo 10.0-3 inverters connected to a
> 208V WYE building hundreds of feet away.  While the building has a neutral,
> I would like to avoid sending the neutral out to the inverters as it is a
> waste of materials. More wire, bigger conduit, neutral kits in disconnects,
> etc.
>
> The Symo manual indicates that there is a wye grid configuration with
> three phase and a neutral. And there is a delta configuration with three
> phase only. Both appear as though they can be set to 208V
>
>
>
> I can't see any reason why I can't program the inverters at Delta and not
> have a neutral. Am I missing anything? I tried inquiring with Fronius, but
> it's a process and the conduit has to go into the ground today.
>
> Thanks wrenches!
>
>
> -James Jefferson Jarvis
> APRS World, LLC
> +1-507-454-2727
> http://www.aprsworld.com/
>
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to